Why couldn't I use address 116?
S7PP
Sep 2010
Toronto
134
I'm doing Hardware configuration on Step 7, S-300, 315-2PN/DP. Insert couple of DI, DO AI and AO module. When I assign them address, I assigned AI1 with 100 to 115, then I tried to give 116 to AI2, but the system doesn't let me, only want me assign 128. I don't have any other module using address from 116 and I checked Address Overview, the 116 to 143 is a gap.
Why is that happening? So wired.
The 315 has a process image of 128 bytes. You are attempting to set the address of the second analogue card so that it straddles the process image and the peripheral area. The h/w config will not permit this.
OH, I see. I didn't realize that. Is that means that I have use PIB/PIW or PQW to access the I/O address above 128 bytes? Is it make the cycle time slower?
Thanks a lot L D.
It is recommended that analog signals are out of process image area. You should address all your analog starting from 128. Yes then you need to use PIW/PQW.
I would recommend the opposite. I would stretch Process Image to 2K In and Out and then all the I/O is scanned at the same time. You can still use PI/PQ commands for quick stuff. Easier to force and will execute more stable scan times.
This is what is done for PCS7 by default. A nice byproduct of this is it allows you to cluster addresses by area or racks.
Rack 1 I/Q 100~199, Rack 2 200~299, MCC's 500 etc
Nick
OH really? I thought adccess PI/PQ is slower than directly access I/O, when you say "You can still use PI/PQ commands for quick stuff." doesn't mean it is quicker, right?
Well I guess it will be neat than use half half.
thanks a lot.
Check hardware manager. It's been a while but I think V2.7 (don't quote me on this) or better.
I'm not running Step 7 on this box and don't have my VM image with me but will check later.
I think he means the peripheral area. He might want to use PI/PQ for all the IOs.
Maybe it's better than use some of I/Q and some of PI/PQ, because the scan time is very different.
Nick you are right, 315PN/DP lets you adjust p image size, but i would still rather use analog in peripheral area. Its 300 series cpu afterall.
You will slow down CPU a little in the beginning by scanning all the I/O but then you will not be doing any immediate reads/writes in mid scan. Read/Writes to I/Q are like working in M area and the stuff gets updated to real world and back during service break at end of scan.
I have had good real world results with this. On large projects.
Nick
hello, I'm working in a project on TIA Portal V13. when I tried to configure my hardware I couldn't my CPU. I checked the compatibility of Siemens...
2,684
Hello, I have Allen-Bradley 4100-234-RL IMC-S/234 Compact Motion Controller, I could connected to controller, but I unable download application...
1,791
Just wanted to post this for anyone who might run into this issue in the future. A couple days ago, I tried to update the RSLogix 5000 that I have...
20,644
Dear Folks, I'm trying to configure a 315T-2DP CPU (6ES 315-6TH13-0AB0), but I couldn't find it in the HW catalogue. I'll appreciate if some...
1,758
Hello Everyone, I am not having very good experience with AB PLC...I have good working knowledge with siemens...We have two plcs 5/60 and...
5,299