Im just finished calibrating a type J thermocouple and it stated in my book that having a live zero was important but it didnt state why. Does anyone know why having a live zero on the converter is important? Any help would be appreciated
Just like the 4ma 'zero' in a 4-20ma current loop. It distinguishes between a true reading of zero (or whatever the lowest reading is) and broken interface/wiring.
I suspect that you didn't calibrate the thermocouple but that you calibrated a thermocouple transmitter, because there is no such thing as a live zero for a thermocouple by itself.
A 4-20mA signal from a temperature transmitter has a 'live zero', where the 'zero' (whether the value is 0 or something else) is 4.0mA. The importance is that any fault that creates 0.0mA, like a broken wire or failed power supply can be detected as a fault by the analog input's receiver device, rather than as a valid reading of 0.0.
When the range is zero to something, this is especially important because the process variable might well be something other than zero.
Transmitters that output 0-5V or 0-10V do not have a live zero.
I have an Allen Bradley temperature switch that I am trying to use in studio 5000. I am getting the message "Unable to interpret the IODD file"...
89
I copied a panel in factory talk HMI for an identical system. The label names are still the same as the original panel but I am trying to change...
146
Hi All, Firstly… Merry Christmas to all of you! Secondly, as some of you may have noticed I made some modifications to our backend to address...
29
7,117
Hi Everyone, I am supporting a system which runs on a SLC 500 (1747-L532). A fault has developed whereby the output state of some digital outputs...
1,017
EDIT: I suppose i should mention, RSLogix 500 V8.40, SLC 5/04 (1747-L542C) Is there is a way to use the FFL instruction in a way that doesn't...
871