Will Panelview plus 6 HMI communicate with PLC-5 on controlnet
YASH_A
Jul 2011
Mumbai
Hi All,
We currently have an existing panelview 1000e(on control net)communicating with an existing PLC-5(Build in control net processor).We are planning to replace the panelview 1000e with the new panelview plus 6 1250 (with controlnet comm card).My query is will this new panelview work with existing PLC 5 ? If not what alternate solution is possible.
Thanks in advance
Thanks for quick reply ..........Additionally ..........
How will be the addressing? If i have to read N7:0 from PLC-5 processor will the format be [nodename]N7:0 or [nodename]N7[0]where node name is PLC-5 node.
Thanks in advance
I would check two details first:
1. Does the PLC-5 controller us ControlNet Phase 1.25 or Phase 1.5 ? The difference will be evident in the part number (ex. 1785-L40C versus 1785-L40C15) and in the method of configuration (phase 1.25 used 6200-PLC5 or AI-5 software, and phase 1.5 uses RSNetworx for ControlNet). I am fairly confident that the PanelView 1000e supported only Phase 1.5, but I'm not certain.
2. Is the PanelView 1000e configured as an I/O connection in RSNetworx for ControlNet, or does it use only unscheduled communications with the PLC-5 ?
As I understand the device, the PanelView Plus 6 does not support scheduled connections on ControlNet, only Unscheduled.
Thank you, fuzzy logic.
I was uncertain about the changes to the PV+ 6; I knew that the RIO Adapter mode was going to be unsupported but RA had not been clear about the ControlNet Scheduled mode.
This is a good thing for you, YASH_A, because it means that your new PV+ will definitely support the same communications with the ControlLogix as it did with the PLC-5C15.
Panelview 1000e had different part numbers for ControlNet phase 1.25 also.
• 2711E-T10C7 (touch screen for ControlNet 1.25)
• 2711E-K10C7 (keypad for ControlNet 1.25)
• 2711E-T10C15 (touch screen for ControlNet 1.5)
• 2711E-K10C15 (keypad for ControlNet 1.5)
Ken is right here, good suggestion to check this first, as the newest platform doesn't support the old Controlnet phase 1.25.
- fuzzy logic
Thank you again ! It's been over ten years since I touched a PanelView "Enhanced", and I upgraded the last ControlNet Phase 1.25 system in my region during Christmas 1999.
He he, what a nice Christmas ! 🙃
I'm "touching" PVe frequently here, to swap them for a new PVP... fortunately never had to deal with Controlnet 1.25 conversion during these upgrades...
- fuzzy logic
I'm trying to use the Create New User button on the HMI so customer has the option to add new users and passwords at the HMI. They dont have...
418
Hi, I have a PVP 1250 with ME station FW 6.0 I would like to upgrade it to ME Station FW10. I downloaded the FW10 from Rockwell site and...
2,294
Hi all, I'm still learning so apologies for silly questions. I have developed a HMI runtime on Factorytalk View Studio V13.00. I have gone to...
3,000
Hi, I just wanted to know the user administration in factory talk view ME. I have around 12 nos of HMI in a factory. Customer wants to configure...
1,125
I am working with a Micrologix 1400 and a PanelView plus Compact HMI. There are some HMI tags that are present in the HMI that is actively using...
2,721