wiring encoder/drive shield wires to control GND bus
unsaint32
Oct 2012
minneapolis
365
At my work, we have Controllogix 1756 L71 with DI, DO, and a servo card (1756-MO2AE). Today, a DI terminal was occasionally not registering input signal. We also noticed that the servo card was not working. My boss concluded that the shield wire grounding on the servo card was the problem. He told me to disconnect all shield wires from the servo card chassis terminals, twist them together and land them on the GND bus that was used for general control voltage.
As you can see in the picture I am posting (it came from the module manual), there are two terminals in each channel for landing shield wires to chassis: #11 for drive wire shield to chassis, #23 for encoder wire shield to chassis.
I don't know what the optional k-module is, but we don't have that.
Q1) Could the the wiring had been switched by accident? (the encoder wire shield to #11 instead of #23. However, even if so, could that possibly cause that big of a problem?
Q2) What kind of problems could happen, now I wired the encoder and drive shield wires to the control GND bus?
Q3) Does anyone know if this servo card has some kind of fuse I can reset?
Thanks.
I think those shield terminals are connected together internally; the reason they are separate is just to give you two screw terminals for the two shielded cables that are typically connected per channel.
That wiring diagram is from a specific application manual associated with a TR Electronics encoder that sends absolute position data via a pulse burst. The K-module was a buffer, I think. That's not the general-purpose wiring diagram for the 1756-M02AE.
I would check the voltage of the DC power supplies, relative to chassis ground, and check to be sure the terminations are secure.
A floating DC common wire would explain both the motion module and input module failure to detect input signals. Unless there is a red OK light, I don't think the module is damaged or faulted.
I'm a beginner and not sure what to do. I want to monitor the rotation of a motor. I have a FX3U PLC and a RI58-O/100 encoder available. The...
1,415
Good day I have to Wire a incremental (1024) Encoder EG7s to a Mitsubishi drive using card FR-A8APA has anyone ever wired this to any drive ...
1,391
Hi, Im a bit unsure about how to connect my SIEMENS encoder (5V TTL/RS422) To my baseunit (The light one).. I have attached a pic of how i have...
1,531
I am rebuilding a line with 2 conveyor sections, that the process speed is calculated from a rate signal from 2 high-speed counter modules. The...
1,490
I have few existing machines with Omron PLCs in them that I need to get the output from an encoder into. There are several output options...
4,058