wiring PLC digital outputs to VFD

Guys I don't think he was necessarily intending to use an external power supply on the drive terminals. I think he was doing something like this


7 VAC
X----------X
OUT0 5
X-----------X



quote]

That was my assumption as well. If he wired 120V to the system, then I imagine he is still trying to put the smoke back in.... Hence the silence on the update.
 
I am so sorry for not updating until now. I got so busy that I could not even touch this issue. I had decided to use interposing relays as all of you had suggested. Thank you so much. The reason I wanted to try my original method was that I found out the PLC had relay outputs. What Brstilson had described was exactly what I was describing. I still think that it would have worked since the relay contacts are just dry contacts, but I didn't trust my knowledge enough to connect VFD's COM terminal to PLC's VAC/VDC terminal. Thank all of you again.
 
The reason I wanted to try my original method was that I found out the PLC had relay outputs. What Brstilson had described was exactly what I was describing. I still think that it would have worked since the relay contacts are just dry contacts, but I didn't trust my knowledge enough to connect VFD's COM terminal to PLC's VAC/VDC terminal. Thank all of you again.

I had a feeling it was something like this, or that if you wired the power from the 12vdc of the drive as the source for the triac module it might actually work. I was grinning reading the thread.

Thanks for the punch line...not as exciting as Lancie's but thanks anyway.
 
Yes.

I got that from an early post, someone assumed you had triac modules.

I thought you were going to take the +12vdc from the VFD to the AC output card AC common terminals and use the triac outputs to switch the 12vdc signals going back to the drive.

I am not sure what would happen. Maybe nothing. Maybe it would have worked. Maybe a little of both. I think no smoke though, nor damage.

If you had applied 120vac to the PLC card output common and the drive terminals, that is a whole 'nother smelly story. Probably a sizzle maybe a pop, some small fire and little smoke, unmistakable smell.

It was all a misunderstanding gone astray awaiting a part number I think.
 
Last edited:

Similar Topics

Hi, I'm using an Allen~Bradley PLC, Micrologix 1500, 1764-24AWA Base Unit and the Allen~Bradley 1769-OB32 DC Output Expansion Card. The AC drive...
Replies
16
Views
25,455
Posted this to Reddit with little success, so I figured I would share it here as well. Very new to PLCs, but figured I would give it a shot to...
Replies
0
Views
149
I'm currently working on a PLC setup and could use some advice on the best way to manage my power supply units (PSUs). Here's the configuration...
Replies
3
Views
428
I need one PLC to receive a signal from another PLC. Can I wire the PLC output of one PLC to the input of another PLC? (same voltage of...
Replies
15
Views
3,976
I'm a beginner and not sure what to do. I want to monitor the rotation of a motor. I have a FX3U PLC and a RI58-O/100 encoder available. The...
Replies
2
Views
1,429
Back
Top Bottom