You are posting on a thread from 4 years ago. Which posting leads you to believe that you can hook 110V (AC I presume) I/O directly to a drive which requires 24VDC I/O? Interposing relays would absolutely be needed.
 
mirror,

It's not too difficult to start a new thread instead of opening one that's almost four years old.

Archie's explanation was for a PLC with 24 VDC outputs connected directly to a VFD. Yours is a PLC with 110 VAC outputs. If you connect them directly to a VFD with 24 VDC inputs you'll let all of the smoke out of the VFD's control board.

To have the PLC control the run, forward/reverse commands to the drive, you'll need to use interposing relays with 110 VAC coils if you stick with the 110 VAC PLC outputs. Use a contact from the relay to switch the 24 VDC signal to the VFD. Alternatively, you could use a PLC with relay contact outputs.

If you want to have the VFD report discrete data back to the PLC, you'll need to have the VFD outputs connected to interposing relays with 24 VDC coils and use a contact from the relay switch the 110 VAC signal to the PLC input module.
 

Similar Topics

For our system using a sureservo drive with Ziplink module, we have a limit switch that will be our "Home Sensor." Should the limit switch be...
Replies
1
Views
1,069
Hello, I am hoping someone can give me some insight on the current wiring of some AC drives we are currently using. A bit of a background. We...
Replies
3
Views
2,901
The B1 and B2 terminals are for thermal relay AND for braking resistor. Doesn't this mean if the thermal relay trips I have no dynamic braking? I...
Replies
3
Views
2,072
At my work, we have Controllogix 1756 L71 with DI, DO, and a servo card (1756-MO2AE). Today, a DI terminal was occasionally not registering input...
Replies
2
Views
2,069
Hello, how are you? Sorry about what I have done to the USA, but it’s my wife fault she told me what to do! I am learning a new trade on the side...
Replies
15
Views
6,873
Back
Top Bottom