Hi
Can Any One Please Explain The Detail Procedure Of Uploading From S7 200/300/400 PLCs And HMIs Using Ethernet Condition Is You Just Went To The Plant And Dont Know Anything Just Want To Upload And See(No Original Program Or Backup With You)...

Thanks All:site:
 
This be a forum of many PLC brands.
Not everyone here will know the ins and outs of the brand for which you are requiring aid.
Just over 2 hrs and a half went by, people browse this forum in their free time. Meaning there won't be someone around here 24/7 to reply within 10 mins of a question being posted.

How to upload PLC's using Ethernet:

Create new project (or use existing on if you want)
Start (windows) > Run > Type in: 's7hwcnfx' then hit Enter (or press OK)
This will open the HWConfig.
In the pop-up press Cancel.
Now you'll have an empty HWConfig screen.
PLC > Upload (or the upload icon) > In pop-up select the project in which you want to add the station.
In following pop-up you can either manually enter the IP-adress if you know it or you can use 'View' to search for accessible nodes.
NOTE: The latter option does not show all the PLC's for some reason.
It takes a while for to find the PLC's so don't worry.
Once it's done it will populate the lower box with the PLC's it found.
Now you just select the one you want and press OK.
NOTE: You need to select the position of the CPU first. Rack is usually 0, but Slot can be 2 or 3 or any other number depending on the actual placement of the CPU.
Either it will give an error saying the Download can only be done through the CPU, or it will start the upload. On Error, it means the Slot was not correct.
It might give an error about the subnet mask, or differing names, but that won't stop the upload.
Don't forget to Save.

Now you have the Hardware, now you just need the software.
Open up the project with the new PLC (will only be visible after you've saved the HWConfig)
Go to Blocks. You'll notice it's empty except for System Data.
Now you'll want to switch to Online mode.
In Online mode, select all the blocks (CTRL+A) copy them (CTRL+C) and paste them (CTRL+V) in the Offline view.

Now you'll have a back-up of he existing PLC.
NOTE: This will be without comments and symbolics.

Any existing connection configured in NetPro will also be available.


Hope this helps.
 

Similar Topics

How can I access the web page that allows me to see and upload the pcl or translation file into my Pl1000E? My Pl1000E doesn’t have an ethernet...
Replies
2
Views
133
Hi guys, I have had some issues with uploading a program from a Micro 850 PLC. This is the first time connecting so I don’t have a file on my...
Replies
8
Views
301
Hi everyone, I want to upload the program from my CPU317TF-2 DP to my PC via connecting to CP 343-1 Advanced since it has LAN ports and the CPU...
Replies
1
Views
174
Hi all, Im stuck trying to support a client with Motorola ACE.. I was able to upload all of the other sites to STS but one. Im working remotely...
Replies
0
Views
115
Hey, i'm getting an error when i try to upload a program from a modicon M258 TM258LF42DT using eithernet. i tried using both SoMachine V4.1 and...
Replies
12
Views
1,328
Back
Top Bottom