Ken Moore
Lifetime Supporting Member
They are using PD files, so should be somewhat easier than the old non-enhanced processors where everything was integers.
You need to change the engineering units to the scaled span of the temperature inputs.
I see setpoints of 511 or so, but the range is 0-4095 EU, not going to work well.
Also for temp loops, the tuning looks too aggressive, too much gain, and too fast on the integral.
Edit:
The PID is setup for raw counts of 0-4095, make sure the analog card setup matches.
You need to change the engineering units to the scaled span of the temperature inputs.
I see setpoints of 511 or so, but the range is 0-4095 EU, not going to work well.
Also for temp loops, the tuning looks too aggressive, too much gain, and too fast on the integral.
Edit:
The PID is setup for raw counts of 0-4095, make sure the analog card setup matches.
Last edited: