0-10V shielding
NetNathan
Nov 2011
Corona, CA
2,199
Does 0-10V signal really need to be shielded if run with 24VDC wiring? How about 120V AC?
Does it rally need to be twisted pair shielded?
I am running a control cable with 10 16 awg conductors inside. It is carrying 24VDC IO and power. Curious about including 0-10VDC signal as pair of the conductors.
Generally speaking, a voltage signal is more vulnerable to electrical noise than is a current signal.
How about 120V AC?
That's an even more critical circumstance. Another thing to watch out for is mixing 300V and 600v insulation in the same conduit. That's a code violation.
Does it really need to be twisted pair shielded?
That's what shielded twisted pair cable is made for.
Assuming that the cable won't be exposed to significant noise, it will probably work, but I'd personally consider it bad engineering practice.
All valid points. I am in an argument with another technician on if it will work and/or is it valid practice.
I thought 4-20mA was more susceptible to noise and also required twisted pair. I do think that 0-10V deserves shielded cable.
Yes, it absolutely should be shielded but the other consideration if it is permissible to run low voltage cable in the same raceway with power wires.
You had better check your local codes and customer specs.
Twisted pair have better immunity to noise than untwisted, I suggest where possible use twisted & shielded, however, in saying that for small length runs probably will not matter I have seen runs of over 50 meters of UTP & non twisted pairs carrying 0-10v on the same tray with two 300mm 414v 3ph cables from a transformer without any problems on the network or analogue signals.
Actually I meant.... is the shielded cable required to carry twisted pair. or twisted not necessarily required.
I have seen shielded cable with 2 wires, not in "twisted pair" formation.
No, not required. It really all depends on how much noise immunity you want/need for the application. Starting with just a basic two conductor cable, each of the following will add an additional layer of protection to noise:
1. Twisted pair
2. Each of the two conductors within the cable are individually foil wrapped (shielded)
3. Heavy foil wrap (shield) around both conductors together as a pair
4. Bare metal 'drain' wire included in the cable
Of course for each one of those you add to the cable, you're adding additional cost. The higher the precision requirements for the measured signal, the more noise immunity in the cable that might be required. There are other things to consider too, such as what, if any surrounding noise emitting devices or wires are in the vicinity, etc. Also, the smaller the voltage signal, the more noise you will see in the measured signal. So if it's a low mV signal you're acquiring, you most definitely want to use the best noise immune cable you can get.
Voltage signals are more susceptible to noise than current signals. However, voltage signals are faster (current lags voltage), which is why it's common to see analog voltage signals used for most high speed measurement applications.
Give it a try, if you already have the cable laid out, put a sensor on one end, hook the other end to an analog input and trace the signal on a scope(be it a physical one, or a virtual one on the PLC).
You could do a lot worse than to read and follow this document:
https://literature.rockwellautomation.com/idc/groups/literature/documents/in/1770-in041_-en-p.pdf
Any current in a wire induces a magnetic field around that wire. Also, the opposite is true, when a wire is in a magnetic field: a current is induced. Twisting the wires helps (can't really eliminate 100%) cancel these currents out to reduce the noise. So running your signal wires parallel to your 115AC wires is putting them in a magnetic field; not twisting them is allowing the induced 'noise' current to effect your signal directly without the cancelling effect of twisting.
Check out the image to see how 4-20mA signals might be more resistant to noise than 0-10V signals for a specific example.
Now, your process may tolerate running next to AC lines. There may be some inherent averaging to your inputs or it just might not matter to what you are doing but best practice is to keep AC and signal separated and to use shielded / twisted pairs for signal wires.
If you already ran the conduit, pulled wire, and terminated. You can always run the 0-10v shielded cable outside the conduit if that is possible. Just tie wrap it to conduit and be done. Not pretty but functional.
Current lags voltage?
It may be that the regulation needed for a constant-current source introduces a slight delay for a rapidly changing analog that would not be present for a constant voltage source. So maybe the idea that an analog current signal doesn't 'settle' as fast as analog voltage signal has some merit. This is a high-speed oscilloscope discussion that is of little interest for PLC work. If you're concerned about speeds like that then a PLC is not the right choice for what you are doing.
Presumably the 10 VDC signal is output from an amplifier (often integral w/ sensor, could be just an op amp circuit). That has high current drive capability, so it is hard for noise to exert itself on the signal lines, since that would need to be a lot of power picked up. I can relate personal experience.
At Westinghouse, we made portable instrument systems to test 480 VAC motorized valves. Strain gages were installed on the valve stems, with ~1 ft of straight unshielded wire about 2 ft from the motor and on-valve control switches before going into a shielded untwisted instrument cable (Belden or Alpha wire) run up to 35 ft to the amplifier and digitizer. The strain gage signals picked up no AC noise from the motor running. I attribute that to them drawing ~50 mA current at 10 VDC, which is 500 mW power draw, since a 350 ohm bridge which is "low impedance". The signal traces did show a glitch when a switch opened in the 120 VAC control circuit. Not from the 480 VAC contactors since those were in the Motor Control Center far away, so likely from switch contact sparks (aka Marconi's first demonstration of RF transmission, spark to spark). But, the techs appreciated those glitches as a time marker, so we didn't improve the wiring.
In later work at Aerojet on a large vacuum braze furnace calibration issue, I found the Type S thermocouple wires (~40 mV max signal) ran straight thru the 480 VAC resistance heater control cabinet. Those are straight unshielded wire (Type S extension wire). That was designed by the vendor. Amazingly, I found no AC pickup from that, though perhaps there was when heaters switched (no concerns). Again, I attribute that to TC's being "low impedance" (effectively a short circuit), so noise sources would require significant power to override the voltage signals (Seeback effect). Indeed, TC's run backwards (apply power) have enough energy to cool, as in the thermo-electric soda can coolers for automobiles.
Long ago, when I first worked with National Instruments hardware, I wondered that they ran the signals from the 5B amplifiers to the PC digitizer board using unshielded, untwisted ribbon cable. The reason that worked was that the amplifier outputs have much drive power, so are effectively "low impedance". However, I did use some NI (or similar) hardware which used special twisted ribbon cable or twisted and shielded (forgot the app). I once opened a precision "charge amplifier" for DC-accurate piezo load sensors, from PCB Piezotronics (or Kistler). They ran the input wires from the BNC inputs in the air directly to the charge amp input, using Teflon stand-offs, because routing them on a circuit board would leak charge. They were probably shielded too. Similar tricks with nano-ammeters, though forgot the details. Many precision PC acquisition boards have shielded boxes over the critical first-stage amplifiers.
Finally, my toughest shielding task was at Westinghouse where we had to qualify our portable system for Euro CE mark (similar to FCC requirements). I spent a week at a testing lab in PA where our system was in a room with a powerful RF antenna sweeping thru frequencies looking for noise pickup on our system ("Susceptibility" requirement). To pass the strain gage sensors, we had to play tricks with cable shielding. You generally don't want to ground a shield at both ends, to avoid 60 Hz "ground loop" pickup, but we found doing so improved shielding to RF emissions. The reason is likely due to higher impedance of the braided shield at high frequencies, so you need as many paths to ground as you can provide along the cable. The hardest to pass was our eddy-current sensors since they used large wound air-coil pickups to purposely sense EM returns, thus were designed to pickup RF. I recall we had to write our way around that susceptibility. BTW, CE mark is a self-validation and only requires keeping a report at a site in a Euro country in case you are audited. You see them on even stuffed toys from China, which are likely never audited. Brexit likely threw a kink since our report was kept in a UK office. In another case, I was setting up our system in Korea for a demo for government nuclear agency visitors. During setup, we were getting high AC noise on the strain-gage traces. I finally found they were using an AC extension cord which didn't have a ground wire (Euro-style 2-pin plugs w/ side ground), so our processing box wasn't grounded, and thus the cable shields weren't. I had them run a ground wire from our box and clip to the motorized valve, then the AC noise totally disappeared. Avoided a big embarrassment. I had warned them about that extension cable earlier. Anyway, we then went with the reviewers to a restaurant then karaoke club, like every night. Like in Japan, working there is more than a job, more like being in a Samurai group.
In sum, if your 24 VDC power is not suddenly switched and is low-ripple, I wouldn't expect any effects on the signal wires. Even if switched, amplified signals may not pickup that, but would have to test. Twisting is more effective than shielding to avoid magnetic disturbances, such as from current flow changes (B-S law), which is why most ethernet cables are UTP (also cheaper). But, 24 VDC might exceed some safety thresholds. I was once called by a young engineer at a USAF Lab I had worked, questioning the safety of some speaker cable I used to wire 24 VDC supply to a level sensor. I told her that I think speakers might see higher voltages transiently. Anyway, that was the only suitable cable I had at home and USAF procurement took over 6 months and multiple signatures from unhelpful Majors, but she was welcome to try ordering better cable. I know that 120 VAC is a safety concern, but perhaps some run it in the same cable with instrument signals out of necessity (perhaps robotics), probably in custom cable with special wire inside.
Does anyone have experience wiring this type of analog pressure transmitter up? It's 4 wires. 3 blacks and 1 green which I assume is earth...
282
I have a SX2 plc and i'm getting 0-10v analog signal,but i need 10bar analog output in 0v can someone explain how its done
550
We have a 4 wire 0-10V analog OPT2012 (Time of flight distance laser) from Wenglor that we're experimenting with. We are able to teach the laser...
555
Hi All, Not strictly PLC, but I'm sure someone works with this stuff and might be able to point me in the right direction. I'm designing a...
1,049
We have constructed a new vibrator control station with local pots on the panel and remote pots on a wireless system. We are running 6 AB 525...
715