1746-NI4 config
islman1975
Jan 2005
How do I configure this card for 4-20ma. There doesn't seam to be an output word associated with the slot when I configure it as I've found when using the 1746-NI8 card.
I dont have the card yet. The dip switch is for either voltage or current. But you can select either -+20mA, 0-20 mA or 4-20mA usally with a cofiguration output word you write to. Well I've done this in the past with the 8 channel card.
they're similar - but not the same -
the NI4 doesn't have the same features as the NI8 ...
the configuration and scaling are different ...
page 4-6 [Adobe Reader page 44 of 113] of the
4-Channel Analog Modules User Manual
should help you understand how the NI4 interprets the different input ranges ...
PS Edit: which is what my distinguished colleague 93lt1 was posting while I was typing away ...
4-20ma
I'm shooting from the hip here, but I think you configure the card for current, which gives you a range of -20 to +20 ma (which I think is not adjustable by any user means). Since your input device (sensor?) ranges from 4-20 ma, the numeric range you'll get from the input will be in the range of 6550-32767 as the input swings from 4-20ma. Use the SCL or SCP instructions to convert these raw numbers into something useful.
It seems to me I've done this..uh...maybe once in the last 6 or 7 years, so I'm going from memory.
rotsa ruck!
CB
Hello all. I have a 1746-NI4/B and I would like to get a cheap temerature module which I could use. I have found this on ebay...
2,607
I have a 7 -slot rack with SLC5/05 1747-L552 Processor. I have configured the inputs on slot 3 as I:3.0 I:3.1 I3:2 I3.3 and have tried different...
1,342
Is it really 0V input? You actually have a signal source hooked up to the input terminals? What does it read if you short the input terminals? Is...
3,042
G'day lads, We are using an Allen Bradley PLC slc5/03 with an analog input module 1746 ni4. we have a sensor with a response rate of 250ms. in...
3,145
I've already found the error and now this problem is solved. But I read about the RSlogix 500 and there was something like convert to BCD (Tod) a...
1,804