1747-ke 5/03 - Df!
Joe_WaZoo
Oct 2006
Murphy, TX
301
Hello,
I have an AB 5/03 PLC that has the DF1 connected to an HMI. I have purchased a 1747-KE card for that rack that I thought I could take the DH485 out of the 5/03 and the 1747-KE would convert that to DF1 so that I would get another DF1 port out of my PLC rack. Has anyone done that? Does there seem to be some ladder logic that I need to write to make this happen? Any advice you could give would be great.
Regards,
Joe_WaZoo
What is the pin-out of the 1747-C13 cable that will allow me to connect to my 5/03 DH485 connection? Can I use an Ethernet cable with RJ45 connections to go between these two ports?
Thanks,
Joe_WaZoo
Success!! I got this to work today. My SLC 5/03 had the DF1 port connected to an HMI. The 1747-KE card was placed in an unused slot on the same rack with a short standard Ethernet cable going from the DH485 port on the 5/03 over to the DH485 port on the 1747-KE. I then had another DF1 cable connected to a DataStation Plus product that put that DF1 on Ethernet for "pass-through" comms to occur from my Laptop with RS_500 to that SLC. This was one of some cool things I got going today.
Joe_WaZoo
hello I am getting a 57h fault - Specialty I/O module has not responded to a lock shared memory command within the required limit. Fault randomly...
95
We are in the process of upgrading a controls system. The existing system is a SLC500 with some IO cards and a 1747-SDN module communicating to a...
553
se me desprendieron los cables del cable usb quiero soldarlos pero no se como van los cables si alquien me pudiera proporcionar una foto o como...
407
Hello, I've got a project where I need to get information from two ABB ACS880 VFDs onto the plant operator's screen (or alternatively, onto...
23
2,614
Hi Newbie here :yeah: Can one of you experts help me with setting up a simple BTR and BTW to just test 4 analogue inputs 4-20ma (1974-if4i)...
1,003