1756-hsc
Wormfood
Nov 2009
Boise, ID
29
I'm using a 1756-HSC counting Pulses from BEI encoder. I get the counts back and in the right direction as expected. Once every so often (happened twice yesterday, couple of time today) the counts just take off. Yesterday it took off negative, this morning the counts took off positive. The line drive light for the correct direction does light up, but the motor never moves. Using shielded/grounded cable. Does not happen on the other 3 that I have hooked up in the same program. Anyone have any ideas?
TIA
Worm
It could be induced noise. I have seen it before. The 1756-HSC should pick up the pulses coming in out of phase or too quickly and generate and error. Apparently it worked in your case because the motor didn't move which is good. Does the 1756-HSC report errors? If so I would check to see which errors were generated. I seriously doubt this is a HSC problem.
It is time to check wiring and get a scope.
I have am trying to determine if I can use a 1756-IB16I (or some dc input equivalent) to handle a 24vdc input pulse frequency of 80 pulses per...
944
Just finished an upgrade from a SLC500 to CLX where they had a 1746-HSCE and we're now using a 1756-HSC. Two wire pulse signal from the...
1,305
I have an older SLC500 that has a PLS card in its rack. I want to remove the SLC and add a L23E-QBFC1. Can a resolver be wired up to the High...
1,691
Our ABB Vision System requires a Pulse Train Input from an Encoder (12-15 VDC)to calculate the speed of the web. Instead of adding an encoder to...
1,574
I am upgrading HSC modules and have some questions. I can't attach the manuals for reference as they are too large. 1746-HSCE uses M0:e.1/4 for a...
1,657