Anyone have experience using this module they can share? I like the idea of retrieving more data from an input channel than the one being read by 4-20mA. I didn't like reading that the update time for HART information is 10 seconds if all 8 channels are HART enabled.

For example:
We use MicroMotion Mass flowmeters a lot and it would be nice consolidate flow, density, and temperature readings on one channel. It would also be nice to be able to read totalizer value and be able to reset it over HART.
 
Last edited:
We have some IF8H cards, but we havent done anything but read the PV, SV and TV over HART. In my opinion, a much better solution would be running modbus to the micromotions. We have about 25 micromotions in our plant, and we get sub second updates over modbus to all devices, on one bus. That would be the preferred installation. I can try some messaging via the hart modules when I go back to work in the New Year if need be.
 

Similar Topics

Does anybody know what the differences are between 1756-IF8H vs 1756SC-IF8H?
Replies
6
Views
3,676
Hi guys, Lately I was involved into a project utilizing 1756-IF8H HART analog modules. Standard features described in module manual include only...
Replies
6
Views
6,522
Good afternoon, I came with a question, currently i have a remote chassis with an series of modules I/O, digital and analog,the analog module...
Replies
1
Views
1,184
Good morning all, We are having a rather strange issue at one of our plants, wondering if anyone has dealt with this kind of problem before. We...
Replies
2
Views
4,468
Hello All, I'm programming a 1756-IF8H to configure a Rosemount 8712E magnetic flow meter. I'm able to read the registers but the AB literature...
Replies
0
Views
1,381
Back
Top Bottom