1769-L32E Date is changing
rocksalt
Aug 2008
Texas
102
I have a 1769-L32E that likes to change its date and time when powering down. It always goes to 2215 keeping the same date and moving the time 1 hour back.
There are no SSV instructions in the program. There are no global connections in the HMI, the HMI time display is correct and the controller is not loading from flash at boot.
Any ideas?
Sounds like it is set for 1 time zone farther west than Texas, or it is not set up for Daylight Savings time, or you have one of these "anomaliles" (Rockwell word for malfunctions) in your CompactLogix Wallclock:
Publication 1769-RN008H-EN-E - September 2005
CompactLogix Controller Revision 13 13
CompactLogix 1769-L31, -L32E, -L35E Rev. 13.21
CompactLogix 1769-L31, -L32E, -L35E Rev. 13.19
CompactLogix 1769-L31, -L32E, -L35E Rev. 13.18
Table 7 Corrected Anomalies
Anomaly: Description: Issue with time reported by real time clock caused controller to transition
to safe state (i.e., clear memory). During normal operation, the CompactLogix controller runs a background diagnostic to verify that the real time clock is working properly. When this anomaly occurred, the diagnostic indicated that the time reported by the real time clock was not what the controller expected it to be. In this case, the controller firmware interpreted the wrong clock time as a potential issue. By design, the controller transitioned to a safe state, clearing its memory and indicating that a major fault had occurred. The transition to a safe state was done as a preventative mechanism.
IMPORTANT: This issue was NOT an issue with hardware or controller memory. Instead, this
issue existed in the firmware diagnostic routine. The firmware revision specified by this release
note corrects this anomaly.
Table 8 Corrected Anomalies
Anomaly: Description: The WallClockTime increased after power cycles.
When the CompactLogix controllers had power cycled, the controller wallclock time increased.
The WallClockTime changed to an invalid value after restoring from CompactFlash at power up.
If you use a CompactFlash card and have it set to “restore on power up,” you may have needed to
reset the wallclock time. If maintaining an accurate wallclock time was crucial to your application,
you either had to disable the “restore on power up” feature or use a combination of GSV and SSV
instructions to check the wallclock time and, if necessary, reset it to a more accurate time.
CompactLogix Controller Revision 13 17
Restrictions The restrictions are organized by the catalog number in which they exist.
CompactLogix 1769-L31, -L32C -L32E, -L35CR, -L35E
Table 11 Restrictions
Restriction: Description: Irregular power cycles can affect the wall clock time.
Irregular power cycles, such as brown outs, can affect the wall clock time. If you use the wall
clock time for critical system timing, routinely synchronize the wall clock time to a master system
clock using a GSV instruction. If you have a CompactFlash card set to “restore on power up,” you may need to reset the wallclock time.
If you use a CompactFlash card and have it set to “restore on power up,” you may need to reset
the wallclock time. If maintaining an accurate wallclock time is crucial to your application, either
disable the “restore on power up” feature or use a combination of GSV and SSV instructions to
I have the compact flash set to restore program only if memory is corrupt. I have no warnings for battery and this issue happened when the CF card was loaded with an old program, which was not loaded.
The version firmware is 19.11
This has me stumped...
I am considering having the panelview write the SSV from it's time as it seems to be the only good time keeper on power up.
Had the same problem on two different machines. After fighting it for awhile i changed the batteries on both. I had no battery light but i was stumped. Has not happened again in over 8 months since battery change. Dont know why but in my case it has worked so far.
I saw your post and grabbed what I thought was the right battery... Never made it back to change it.
I will put one in tomorrow but I wont see it happen now unless I remove the logic I added. I am using the first scan to block the part count rung for 5 minutes to allow the panelview to come up. Then I write the time from panelview to wallclocktime. Works like a charm but I really do want to get to the bottom of this.
I will post back tomorrow.
I just found two old 1769-L32E controllers in the plant that I cannot go online with using my version of Studio 5000 (30.14). I've reached out to...
2,039
Help! I have a compactlogix 1769-L32E running RSLogix 5000 rev 20.14 that keeps losing the date and time when we cut of the power!!! I have...
2,214
Hello, I have a compact logix 1769-L32E that intermittently loses the date and time wihtin the processor. It has reverted back to the same date...
4,549
New module had program in it version 19 wanted to upgrade to 20. During multiple downloads the module was reset to factory firmware 1.15. Now...
1,925
I have been trying to update the firmware multiple times now and still no luck...help! I have it connected on the network, I can see it fine but...
8,167