315-2DP + IM360 + 343-1 Not going to run
Greg Fowlds
Apr 2004
Currently, Waiheke Island, NZ
123
Have a strange fault issue.
New system ran for 3 days then cpu faulted out with vague error messages.
Rack make up is.
315-2DP
IM360
343-1
341 Rs232/485
I/O modules modules
In remote rack
IM361
I/O modules.
Started with blank project with all modules at default settings, no program installed to isolate programming errors.
CPU not going to run.
Remove 343-1 Ethernet module. (rehash Harware setup and download)
CPU goes to run.
Replace 343-1.
Remove IM360. (rehash Harware setup and download)
CPU goes to run ok.
As long as only the IM360 OR the 343-1 are installed, no problem.
With both installed, will not go to run.
Fault log along the lines of:
Parameter assignment error.
No relevance for user: SDB 1001
Nothing there to point at which module.
Replaced 343-1 module, still the same.
Have checked all pins on base of cards, checked power supplies etc.
Have tried with just CPU and Ethernet, OK
Have tried with just CPU and IM360, OK,
Try with both and faults.
Attached log.
This is with only in rack and HW setup without errors at default settings.
6ES7 315-2AH14-0AB0 (315-2DP)
6ES7 360-3AA01-0AA0 (IM360 to next rack)
6GK7-343-1CX10-0XE0 (Ethernet comms)
Event 1 of 106: Event ID 16# 49A0
STOP caused by parameter assignment error or unpermissible difference between preset and actual configuration: startup disabled
No relevance for user (SDB no.): 1001
No relevance for user (Z2): 0000 (Z3): 0000
Previous operating mode: STARTUP (warm restart)
Requested operating mode: STOP (internal)
External error, Incoming event
09:37:14:937 am 06/08/11
Event 2 of 106: Event ID 16# 4301
Mode transition from STOP to STARTUP
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
09:37:14:872 am 06/08/11
Event 3 of 106: Event ID 16# 6547
Parameter assignment error assigning parameters to modules (not on P bus, cancel download)
no relevance for user: SDB number: 1001
DP master affected in rack 0 and slot 4
Station number: 0, slot number: 10
Operating mode: STOP (internal)
Internal error, Incoming event
09:37:14:831 am 06/08/11
Event 3?
Note:
Ran for 3 days without fault.
CPU + 360 = No errors and runs.
CPU + 343 = No errors and runs.
CPU + 360 + 343 = Not going to run.
There is a problem with reaching the CP342-5.
There is mentioned a DP master in slot 4.
Is the CP343-1 in slot 4 or in slot 10 ?
Do you have any connections configured in NetPro ? In any case recompile in NetPro.
Post a screenshot of your HW config.
No connections in net pro.
recompiled in net pro.
Still the same.
Replaced CPU, still the same.
Can only be the IM360 module now,
Possbility the IM360 is not passing the "P Bus" to the ethernet module as Ethernet module not visible from CPU.
Problem is finally resolved.
After working with Siemens support in Australia, was passed to Siemens Germany who eventually could not find the reason for the Fault.
Last comment from them was that my Step7 was too old.
A new IM360 module was sent after some pleading which solved the issue and CPU happily running again.
Dear sir, I am using SIMATIC 300, CPU 315-2DP , (6ES7 315-2AF03-0AB0) VIPA 603-1CC21 A1.0 RAM 32KB, Firmware=V4.0.8 The problem Im using MPI...
211
Hi , Looking for some help. We have a 343-1 PN Lean Card & 315-2DP connected to an external system collecting data. After a recent shutdown...
80
I'll preface this by saying this is the first time I've worked on a Siemens system and I'm fairly unfamiliar with them. I might mess up some of...
29
890
Hi We were having a few power cuts and the CPU would not work. I had to reset the memory and he CPU would read from the memory card and start...
3,239
Hi! I have never cross this kind of problem.. I have kind of working program on 315-2dp cpu. Program has been working nearly 20 years like this...
2,452