Greg Fowlds
Member
Have a strange fault issue.
New system ran for 3 days then cpu faulted out with vague error messages.
Rack make up is.
315-2DP
IM360
343-1
341 Rs232/485
I/O modules modules
In remote rack
IM361
I/O modules.
Started with blank project with all modules at default settings, no program installed to isolate programming errors.
CPU not going to run.
Remove 343-1 Ethernet module. (rehash Harware setup and download)
CPU goes to run.
Replace 343-1.
Remove IM360. (rehash Harware setup and download)
CPU goes to run ok.
As long as only the IM360 OR the 343-1 are installed, no problem.
With both installed, will not go to run.
Fault log along the lines of:
Parameter assignment error.
No relevance for user: SDB 1001
Nothing there to point at which module.
Replaced 343-1 module, still the same.
Have checked all pins on base of cards, checked power supplies etc.
Have tried with just CPU and Ethernet, OK
Have tried with just CPU and IM360, OK,
Try with both and faults.
New system ran for 3 days then cpu faulted out with vague error messages.
Rack make up is.
315-2DP
IM360
343-1
341 Rs232/485
I/O modules modules
In remote rack
IM361
I/O modules.
Started with blank project with all modules at default settings, no program installed to isolate programming errors.
CPU not going to run.
Remove 343-1 Ethernet module. (rehash Harware setup and download)
CPU goes to run.
Replace 343-1.
Remove IM360. (rehash Harware setup and download)
CPU goes to run ok.
As long as only the IM360 OR the 343-1 are installed, no problem.
With both installed, will not go to run.
Fault log along the lines of:
Parameter assignment error.
No relevance for user: SDB 1001
Nothing there to point at which module.
Replaced 343-1 module, still the same.
Have checked all pins on base of cards, checked power supplies etc.
Have tried with just CPU and Ethernet, OK
Have tried with just CPU and IM360, OK,
Try with both and faults.
Last edited: