5/02 and a Panelview Plus
Sep 2008
Ellwood City
Got a 5/02 and a 2711P-B7C22A9P Panelview. How can I add ethernet to the 5/02 cheap for the Panelview? A gateway is too expensive, same thing for a 5/05. Had to replace a panelview and the old DF1 isnt supported anymore. Net-ENI? If so, not sure what cable to use.
Thanks!
(Edit) I think I just got the award for lurker status, lol. Joined 2008 and this is the first post.
Unfortunately your SLC-5/02 has come to the end of it's practical useful life if you need to connect a PanelView Plus 7 Performance terminal to it. A service life of 25+ years is pretty great for any electronic device.
In my opinion, a used SLC-5/05 16K controller is the most practical solution because it requires the least labor to implement.
PV+7 Performance has no serial port built-in or add-on, and it is unlikely that there is an affordable Ethernet/DH485 gateway that is compatible with the FactoryTalk Linx drivers the PV+7 uses.
I very seldom recommend the EquusTek devices because of their long history of misconduct and poor engineering support.
To my knowledge the 1747-UIC is not compatible with the PanelView Plus 7, though that might be worth examining especially with a Forum member (PLCCables.com) who might weigh in on testing the popular and affordable aftermarket version.
I'm not sure that you really have any other options outside of a gateway or upgrading to a 5/05 processor. Serial to ethernet gateways/converters shouldn't be that expensive. I did a quick Google search serial to ethernet gateways and found several for under $250. I am not certain if this solution would work, though.
Automation Direct, StarTech, Phoenix Contact are some brands you could look into.
If you were considering a ControlLogix Gateway, then yes, that would be expensive but not necessary.
The problem is that the SLC-5/02 doesn't support a tidy asynchronous serial protocol, but rather the proprietary and finicky Data Highway 485.
If this were a protocol that had ASCII delimiters on the end of each packet or even was handled by timeouts, that would be different. But DH485 is a multi-station token-passer with low-level timing requirements on switching Tx to Rx.
The 1761-NET-ENI or its equivalent from plccables.com would work with any SLC-5/0x that has an RS-232 Channel 0 serial port, so that's the SLC-5/03, 5/04, 5/05 but not the 500, 5/01, or 5/02.
Kind of what I thought.Was trying to avoid a 5/05 as new cost is $8,800. Going to try to find used but I can't do Ebay, it has to be a company because we will need to set up a vendor account. Used on Ebay runs around $1000... that I can do, $8,800 I can't.
Thanks for the replies!
95
Hi Everyone, Currently we have three plants running with Controllogix PLCs (L72, L73, L74). In each of these plants we have 2 FTView SE...
59
Hello All! Ok, we got a Work cell from a Integrator that is sending saved scanning data from the PLC to HMI (Panel View Plus) when I look at this...
89
Hello everyone. This is more of an HMI issue. I have a new PanelView Plus 7 Series B. I am using the alarm list object to display the fault...
93
Hello, I made a change in alarm setup in factory view studio, where I changed a alarm message text. After that I made a run application and...
141