5/03 Fault

shawnhimself

Member
Join Date
Oct 2006
Location
LBC
Posts
84
I'm attempting to upgrade a 5/02 AB SLC 500 to a 5/03. However when I stick the 5/03 processor in and attempt to put the processor into run mode I recieve a FAULT (invalid rack configuration).

After speaking to AB about the problem they convinced me the rack was bad. So I went and bought a new rack...only to have the same problem. I also tried to upload a blank program and try it. Same result. Same fault. I am able to see the processor with linx, upload, download, etc. I just can't put the processor into run mode without fault or configure the I/O.

Any ideas?
 
The way to be certain that your Chassis and I/O configuration is correct is to connect RSLogix 500 to the controller while offline and use the "Read I/O Config" feature.

Does the controller indicate a numeric fault code ? That will help narrow things down.

One other thing... never, ever remove or insert an SLC module under power. You can blow all kinds of components doing that.
 
I get the "invalid rack config" fault when I'm offline and attempt to 'Read I/O Config". I'll check tomorrow when I'm back at the plant to get the exact fault code.
 

Similar Topics

We had a site where a rat gnawed through some fiber optic cables which (obviously) prevented communication to a remote rack entirely. We, and the...
Replies
3
Views
95
Good morning everyone I’m currently working on a omron device net and have a nord drive that fell off the network. I have limit knowledge in...
Replies
2
Views
90
Hi. We've been asked to do an upgrade on plant, consisting on a PLC upgrade. This involves replacing a 1747-SDN module to a 1769-SDN, in a network...
Replies
0
Views
69
in allen bradley kinetix 300 drive first E31 error shows after resting drive E11 error occurs need solution to reset E11 fault code
Replies
4
Views
160
All, I have a PowerFlex 525 driving an agitator motor. The goal is to have the agitator start automatically after a power loss or a comm loss. I...
Replies
2
Views
107
Back
Top Bottom