525 Faceplate and AOI:
Morning All.
I wanted to start a thread to talk about the faceplate and AOI Rockwell offers for
Factory Talk View ME to control their 525 drives. I downloaded the package from AB .com. It
contains numerous files including a main routine, parameter file, goto button, .gfx file and a user manual.
Issue #1. No alarming on configured project.
"""Configuration of “Fault_Msg” instruction.
Select :
Service Type: Get Attribute Single
Class : 97, Instance : 4, Attribute :1"""
This is a clip taken from the user instructions on page 13.
These values are incorrect and should be, Class : 93, Instance : 7, Attribute :9.
Issue #2.
Speed Reference:
I have attached a screen shot of the speed reference rung after I modified it to make it work. In the original as downloaded
AOI that CPT instruction for the speed reference had the tag "speedRef_Units" instead of the tag "SetSpeed_Program".
Likewise, the next rung in the AOI shows the operator speed refernce using the same tag "speedRef_Units"
in its CPT instruction. The odd thing here is that the speed refernece entered in on HMI faceplate in the operator mode sends
its speed reference value to the tag "speedRef_Units" and not to "SetSpeed_Oper" as I would expect.
Issue #3.
Displaying of values:
I am noticing that on my HMI faceplate when in run time. I see the frequency, current voltage and speed displayed with the wrong
decimal. Example: If current is 5.61 on the HMI I see 56.10. There are many instances of this in a single faceplate.
SO as you can see I have had a few issues with this AOI trial project. I expected to get a little more feedback from Rockwell on
this but it has been a while and I have not heard back from them. NS_Drives_Guy, I'm looking at you!! I simply want to know, were these AOI/Faceplates meant to be
"ready to go " as downloaded or is there expected reconfiguration of the AOI to make it work. I would think that things like multiplier
values would already be set to look at the 525's two decimal configuration. Perhaps there is something I am missing in setting these
values to display properly but they do not appear to be variables in the AOI.
As for the speed reference thing, I don't see how it could have possibly functioned as written except in the operator mode.
I am left wondering if I should use the faceplate again as it was not as seamless as I had hoped.
Any comments or criticism is welcomed.
Yeah i feel your pain we just had some new equipment installed and the scaling for the speeds of the drives are all wrong. For example, if i open the drive faceplate it asks for Hz as a speed input and if i enter 60 Hz for the speed the drive actually tries to run at .60Hz. To get the drive to run 60Hz i have to enter 6000 on the drive faceplate. This isn't a big deal for myself but for the operators or maintenance it causes problems because the faceplate is asking for Hz.
I would probably just take a couple of hours to fix their mistakes and create new faceplates that have what i need on them and put it away in my sample code folder for later use. It doesn't surprise me that the faceplates aren't correct. I doubt they actually test the sample programs.
I realize I am replying to older post, but this is relevant my current issue. I am using V31 of Logix, 11 of FTVME, and V5 of a PF525EENET. I have faceplate created and can start and stop my drive, but still trying to wrap my head around what else I need to map between the AOI and the AOP. I am seeing the same issue you described with the speed reference. Would you please repost the screen shot you mentioned in this post. I don't think it is available any longer?? Any other advice on this topic would be greatly appreciated. I want to control four 525s that are driving pumps.
Thank you,
Hi, I need to set up a mixing station with 7 PF 525s. All I need is start, stop, forward, reverse and a fault message. Each mixer should be...
4,600
I m doing my first project in RSLogix 5000. I m using the AOI Faceplate for PowerFlex 525 EENET drives. With a compact logix L33ERM controller and...
1,924
Fairly new to the drive so apologise for the layman terms. Textile machine uses PF525 VFDs to control motors. The speed of the drive is currently...
137
135
121