AB L36ERM Connection to Vacon via Ethernet/IP
Johnny Boy
May 2013
WA
Hi Guys,
I have been asked to integrate a machine with a vacon vsd into a control network. It is a vacon NX and the option board is an OPTCI.This board is a MODBUS/TCP option board. The machine builder says it can communicate via Ethernet Ip.The manual for the option card refers to Ethernet ip as well as Modbus set up. I have tried to set it up in the I/O tree in RSlogix 5000 V20.1 as a generic Ethernet Module but I can not set the input and output assembly in the manual it shows as not used. The manual is very vague and when I look on the net for vacon I keep getting redirected to the Danfoss web site. Do I need to use a pro soft MV169E-MBTP?
Thanks in advance for any feed back!:site:
MV169E-MBTP has only serial ports. For Modbus TCP/IP application you have MVI69-MNET:
http://www.prosoft-technology.com/P...-TCP-IP-Communication-Module-for-CompactLogix
http://www.prosoft-technology.com/c...55/version/15/file/MVI69_MNET_User_Manual.pdf
Prosoft modules are integrated in the Logix I/O tree using a generic module. Also Prosoft provides the logic to run the communications. You only need to design your communications table (registers to be read/writen on your remote I/O).
I found the manual for OPTCI here:
http://www.vacon.com/ImageVaultFile...OPTCI-Modbus-TCP-Board-User-Manual-DPD009.PDF
I think if you know about modbus specifications, you have all the tools you need to start the integration.
By the way, I think you would must consider adding a hardwired stop signal from the PLC to the VSD.
Can you point where does it say that it supports Ethernet/IP protocol?
It looks like this car supports Modbus TCP only.
You may be able to use Modbus TCP Sample code via Sockets or Prosoft Modbus TCP card.
Hi Guys, I want to connect my 1769-L36ERM to a different network domain, is it possible to do it using only the dual ports in the Controller? Or...
226
Hi there, Just a quick question. I have CompactLogix controller L36ERM that gives me energy storage fault. Controller is running fine. However...
452
Does anyone know how many connections are available on a 1769-L36ERM Compactlogix? I have one that is connected to an Ignition SCADA system that...
833
Dear all, Im using Allen Bradley Compact Logix L36ERM as a PLC. and facing a problem where I need to create a FIFO buffer that fills an...
1,661
I cant get my L36ERM to recognize any expansion I/O (1769). Is this a processor revision issue. I had to update firmware on the processor ,when it...
3,776