I am having an issue with a Automation Direct 110V AC Input Card(D2-16NA). This is connected to a Automation Direct D205 CPU. I am experiencing an Input Node failure. I am on my third Input card in the last month. This is on my safety circuit which contains 7 solid state switches. The backplane seems fine and I do not see any cracks in the switches. Has anyone come accross a similar problem?

Regards
 
Check the backplane receptacle where you plug in the input card. It has happened that a little piece of paper or lint gets jammed into one of the pin positions and intermittently blocks it. Those intermittent problems are a pain.

I once was in a computer troubleshooting class where the instructor deliberately stuck a piece of paper on one of the card connectors, and challenged the class to troubleshoot the PLC. Boy I will never forget that one.
 
Make sure that your voltage is not being spiked by the switching of the solid state switch or other parts of the circuit. The inputs on that card are rated for 130 Vac max anything above that and it pops.

Most siemens and ab modules have built in spike protection into the module. The AD modules do not.
 
I checked the backplane yesterday and everything looked fine. I am going to order a backup so I can change out the next time it happens.
 

Similar Topics

Hello All, After trying to transfer some field changes on the safety scanner microscan3, and verifying, the device is stuck at .... waiting for...
Replies
0
Views
45
I have a 120V relay, 120V DI card and a analog input. I was wanting to know if i could put a 24V DI and well as a 120V DI card on the same plc...
Replies
1
Views
87
Hello, I'm looking for a dirt cheap digital display + input, that would be wired to an analog input and analog output. This would be for my home...
Replies
10
Views
263
Hello, I am trying to read a barcode scanner input using a cognex dataman 280 barcode reader, store it another string, the compare with another...
Replies
1
Views
87
All, I have a PowerFlex 525 driving an agitator motor. The goal is to have the agitator start automatically after a power loss or a comm loss. I...
Replies
2
Views
91
Back
Top Bottom