Adding a rung in online mode control logix
spidermonkey
Member
Join Date
Dec 2009
Location
in
Posts
30
I am still new to control logix, I am trying to add a new rung in the ladder with a new tag in it also can this not be done online.
I have made other changes online but never added a new tag or rung on this plc.
I don't get the accept rung thing to press
it has an older L55 processor in it.
After you enter the new rung, right click on any of the new tags involved and make tags out of them. The right click menu should offer a line that says "New 'whatever_your_tag_name'"? And if you choose that, and be careful that you pick the right data type, scope, and array size (if applicable).
That should take care of any tag issues. I have heard reports of the verify button getting stuck greyed out for other reasons, but the right click menu (on the left of the rung) should tell you if the rung is ready to be accepted.
Similar Topics
See picture. I want to add a rung (magenta) into the existing code. Can't figure out how to do this. I select a -||- , right? When I drag/drop...
Replies
21
Views
1,815
Hi, I use Excel to write some routines and was wondering if it is possible to add rung comments when doing so? Excel function: ="MOV "&[@[Range...
Replies
2
Views
2,554
Hi Everyone, Currently we have three plants running with Controllogix PLCs (L72, L73, L74). In each of these plants we have 2 FTView SE...
Replies
0
Views
64
Hello, Im building project with 1756-L82ES controller and 1756-IB16S card but i cant find it when trying to add the card to IO configuration...
Replies
3
Views
144
Hello, I have a pair of redundant 1756-L71 controllers rev 24. These controllers currently have produced and consumed tag interfaces to 3 other...
Replies
2
Views
176
Back
Top Bottom