lupercus23 Member L Join Date Jun 2012 Location ******* Posts 2 Jul 31, 2014 #1 In my 1746-NIO41 analog input card , for a full 20mA input , the reading shows only 16383 ,why is it so ? for input address "i:3.1"
In my 1746-NIO41 analog input card , for a full 20mA input , the reading shows only 16383 ,why is it so ? for input address "i:3.1"
(8{)} ( .) Lifetime Supporting Member Join Date Apr 2004 Location Israel Posts 625 Jul 31, 2014 #2 That's the range for current inputs. -20 mA to +20 mA has the range -16,384 to +16,384 Yosi
lupercus23 Member OP L Join Date Jun 2012 Location ******* Posts 2 Jul 31, 2014 #3 i figured it how .
Mickey Lifetime Supporting Member Join Date May 2003 Location Palmdale,Ca Posts 10,661 Jul 31, 2014 #4 See pdf for raw data for both input and output for your card.