Hey,

I have a problem with the above mentioned anolog card from siemens
S5. In a PLC program, i have to rewrite, they just send a DW to an QW. This is the QW from the analog card. And in the DW they put a value. With this ouput they control the speed of a motor. Now my question is don't you need to scale the value in DW like in S7 before you send it to the output? Or is it that the anlog card scale the value by itself and that you setup the upper and lower limit in the hardware of the analog card ?

Thank you

greetz
 
Hi

If I remember correctly the values for an analog output is between 0 and 1024... So if your value is 0 to 100% then you will have to multiply by 10.

Eric
 

Similar Topics

Hi looking to install a smaller less sophisticated PLC for fountain timing and also one analog pressure sensor which would be used to detect...
Replies
23
Views
639
Hi all. I have 1793-IE4 (4)analog inputs modules in a 1794-ADN IOFlex DeviceNet Rack. I cannot find if I can I have access to individual channel...
Replies
1
Views
75
Good afternoon, I am currently working with an HMI/PLC LP-a070 and I require at least one analog output, but the PLC does not have one. I was...
Replies
5
Views
153
Hi all. Customer wants analog faceplates really bad, even if we explained that it doesn't make much sense in his process. What he wants to see...
Replies
7
Views
263
I'm having trouble calming down 2 Tempo Sonics. I'm using Studio 5000 CompactLogix my Raw value is jumping around from 8575.0 to 8755.0 at a...
Replies
30
Views
1,258
Back
Top Bottom