I am working with a SLC 500 plc (1747-L40A)with a two slot expansion rack. In slot one of the rack I have a 1746-IB16 input card. I have a BCD thumbwheel wired to this card. I programmed a clock using a timer for seconds advancing a counter for minutes that advances a counter for hours. I want to use the input from the thumbwheel to go into the preset of the hour counter to control turn an output on after the counter has reached the setting of the thumbwheel. I have tried to take the input I:1.0 and use it as a source for a FRD instruction and specify S:13 or N7:0 for a destination. When I enter any of these values it shows them as valid entries, but when I verify the program or try to go on line the value I placed as a source (I:1.0) is always changed to S:13. How do I get the value shown in I:1.0 from the thumbwheel into a register I can use. I am following the example on page 1-50 of Rockwells SLC 500 processors documentation reference guide. What am I doing wrong
501 Limitation
With the 5/01's the destination of a FRD must be one of the math registers, the processor has two, S:13 low word and S:14 high word, which can be used together for a 32 bit word. However in your case you don't need the 32 bit, so try the following and see if it will function as a workaround.
Clear S14 First!
Consider this:
Warning! If the math register (S:13 and S:14) is used as the source, and the BCD value does not exceed 4 digits, be sure to clear word S:14 before executing the FRD instruction. If S:14 is not cleared and a value is still in this word from another math instruction, an incorrect value will be placed in the destination word.
Rockwell Software 2000
hi... i have an issue in s7 300 plc, while we run the machine(in idle there is no fault) , plc cpu goes in SF mode, after restart the power cycle...
144
Hi. I’m doing a PV 1400e to PVP 7 migration and I don’t know how to convert the old 8digit BCD type from PB1400e into something that will work on...
600
I'm working on converting an old PanelBuilder 1200 HMI application into FactoryTalk View ME. The PLC was an old SLC 5/02 with a scanner card for...
1,119
I have a Cmore screen which is communicating to the DL06 in BCD and need to create a timer that works in real numbers for a test, I simply need to...
2,168
Hello, I am stumped on how to tackle this issue. I am working on an Energy project on a solar / wind farm and I am trying to read in some data...
2,483