Blown analogue input... Siemens cpu
userxyz
May 2002
any
2,768
Today I had a Siemens PLC 314C with an analogue input that was reading 32768 while having 4mA. So the input is defective. I connected on an other analogue input en all okay.
Several months ago it was the analogue output of the softstarter (same analogue signal that we're talking about) that was broke. We had to replace the softstarter because this analogue signal is a really important one that regulates conveyors.
This is not normal... analogue output and now the input on the other side...
The Altistart takes around 1000 AMPS at Start-U :unsure:
The analogue signalcable is a shielded one, but the shield isn't connected on ground, normally it should on one side I think. Could that be the cause of blown up analogue inputs and outputs ?
How can I protect my analogue in and out ?
Thanks in fwd
regards,
Gerry
Yes, ground the shield at the analog output side.
Does the softstarter supply the power necessary for the 4-20mA signal?
Or does power come from the Siemens AI connections?
Or is a separate power supply needed?
Is where the DC power for the analog output grounded at some point? Can the ground be lifted?
I've blown the Output Transistor on the Output Card of a Compact Logix 1769-L24ER-QBFC1B It says J378. Does anyone know the replacement part...
207
Hey everybody, Would hooking the negative side of a braking resistor terminal (There is no resistor installed) to ground cause a VFD to fail...
669
Monday, we had a VFD that controls the spped of a conveyor belt fail on us. Took the replacement out of the box, installed it and bam, it failed...
37
16,927
Currently using a AB 1492-FPK2, plug in fuse but now finding alot of these are.. touchy with connections. the terminal block they are plugged into...
1,360
Hello Everyone, In need of some most needed help on troubleshooting a Kinetix 6000 servo. The first one smoked and was replaced only to smoke...