Can't Go Online in Studio 5000

TheColt46

Member
Join Date
Oct 2023
Location
Arkansas
Posts
23
Ever since I had to change PCs and redownload all my AB software I have been unable to go online with a controller via Studio 5000. I used to be able to connect with the provided cat6 cable at my station as well as the company Wi-Fi. Neither of these work now. However, I AM able to go online if I use my personal hotspot on my phone and get into the network using our company's cisco VPN. Why this works and not the other ways is beyond my very minimal experience with networking. I have tried to manually set my ipv4 address to the same range as the controller and no luck. I even tried to duplicate the DHCP address that was given to my hotspot connection and try that as my address for my hardwired connection. No Luck. I know I must be missing something very simple but I'm out of ideas.
 
Not a VM. I have not messed with adapter settings beyond changing IP, subnet, gateway, dns. Is there something else in there I should be looking for? Thanks for the quick response.
 
Are you on the same subnet as the PLC? Or going through a router.

If you are same subnet, you can use the ETHIP driver in RSLinx. But if you're routing, you have to use the ETH driver and specify the addresses of the PLC's in the configuration table.

The fact your VPN works is a big clue: what network does the VPN put you on? What's the gateway?
 
Can you ping the PLC while connected to Wi-Fi or the hardwired connection ?

Is there any chance that the VPN and your wifi/cat6 cable are different VLANS ?
 

Similar Topics

I have a device that is communicating to ControlLogix L83E. During apply of online edits to plc, the communication to the device is increasing 4-7...
Replies
3
Views
1,184
Good Morning , I went to edit a rung , and for some reason I can “ Accept Pending Rung Edits “ , but I can’t assemble rung . I...
Replies
17
Views
6,330
Hi All, I am having an odd issue, need help now!:bawling::bawling::bawling: The studio version is 32.13, drive add on is 5.08. PLC is l36erms...
Replies
3
Views
1,859
Hello Guys, I have just upgraded an older machine from a old processor to a new studio 5000 processor (1756-L83ES). For some reason when I am...
Replies
4
Views
3,649
After migrating a SLC to a 1769-L36ERM, the Studio 5000 interface was almost unusable. I started with v24, and then changed to v30 with no...
Replies
8
Views
6,420
Back
Top Bottom