Compact I/O expansion cable between cabinets
kolyur
Oct 2004
Wooster, Ohio
1,602
I have a Micrologix 1500 system that I'd like to expand by using a 1769-PA2 power supply and 1769-CRL3 expansion cable. The problem is that the base and expansion racks need to be in separate cabinets, and the expansion cable has a large I/O endcap on both ends. I'd have to cut a large rectangular hole in both cabinets and use Roxtec-style cable entry seals for it to work as-is.
That is, unless the endcap could be removed from one end temporarily. Has anyone done this? The terminations are hidden by a seemingly removable plastic cover, and I can see at least part of a pluggable rectangular header underneath. I'm hesitant to tear into it unless I hear that it's been done successfully before.
The end cap easily comes apart and the cable pulled through 3/4" conduit. I ran into the same problem. The cabinets will have to directly adjacent to one another. You will also have to take into consideration the right-left left-right expansion cables. Not he best way to do things but can be done.
We have an AB PLC that has a faulty expansion cable between Bank 1 and Bank 2. Part # 1769-CRR3. I found a small burn mark on the board. Being...
769
Does Allen Bradley offer any way to increase memory in a Compact Logix 1769-L32E controller? I need to make modifications in a processor which...
4,748
Hello Everyone, I have a issue with communication between two different PLCs. So here is the facts, The Master PLC is Guard Logix 5069 with IP...
107
What happens if you power up a 1783-MS10T with a Compact Flash card from a 1783-MS06T? Does it work, but with the "extra" ports unconfigured? If...
89
gents, I am trying to configure communication with EMERSON PK300 controller through port A1 using generic ethernet communication module . I could...
118