Yes thats the nice feature about Logix. You don't need to write logic to communicate between to PLC's. Just create the tags using the proper data type, make sure the 2 PLC's are on the same network and setup the properties of the tags. The consumer does most of the work. The producer just lays the tags out there for anyone wanting them.