any help please ,
i hav compactlogix+devicenet scanner + flex I/O , i tried to communicate betwwen pc and plc after updating it .when i refresh rslink classic i can't find the processor ,i find just the scanner and there is a yelloo "?" in the beggining of the processor what does it mean , and when i ping i find the address IP of the processor .thank you
 
Welcome to the Forum, Khaled.

It is very likely that you need to register a new Electronic Data Sheet for the CompactLogix processor that matches the firmware you loaded into it.

Download EDS files from the Rockwell Automation EDS server:

http://www.rockwellautomation.com/resources/eds/

Select 'Network Independent', then 'Programmable Logic controller' then Bulletin number '1769' and the major revision of firmware you installed.

Download the resulting EDS files to your desktop, then register them with the RSLinx Hardware Registration Tool. Launch that from the Start menu; Start -> Rockwell Software -> RSLinx -> RSLinx Tools.

EDS files are also usually updated when you install a new version of RSLinx Classic.
 

Similar Topics

Hello . Info: Panelview plus 400 2711P-K4M20D Compactlogix 1769-l32E i make a program in RSlogix 5000 and Factorytalk view for...
Replies
9
Views
1,823
Hello again. I need to flash a CompactLogix L32E from firmware ver15 to 16. It has several Panelview Plus's Series D Rev A, connected via...
Replies
16
Views
2,807
Hello. I am trying to establish communication between CompactLogix 1769-L32E and CompactLogix 1768-L43 using serial port but with DeviceNet (and...
Replies
6
Views
2,787
Respected sir/madam I have CompactLogix L32E And I want to data log into logic . is any module or card require to it. request you guid me and if...
Replies
4
Views
1,409
A new member of our Forum community, maheshbhaiya, posted this as PMs and a resurrected thread, so I'm going to give it a push in the right...
Replies
1
Views
2,102
Back
Top Bottom