I want perform the comunication (ethernet) between ML 1400 (IP: 192.168.1.11)and Red Lion HMI G304k200 (IP: 192.168.1.20).
I wrote the secuence in the PLC and two tag to test the cominucation, I want activate the B9:3/0 with the HMI and read the C5:3.ACC from PLC but I cant and I have 3 days trying.
I add programs of the PLC and HMI, please, check it and tell me that I am doing bad.
Thank very much for your support.
Best regards.
I noticed that you still have DHCP enabled on the MicroLogix 1400 Ethernet port. Are you absolutely certain that it is getting the same 192.168.1.11 IP address every time you power cycle it.
I prefer to use Static IP addresses, so I disable BOOTP and DHCP.
Also, you are using the "Allen-Bradley DF1 Master" driver in Crimson 3.
As I understand it, the appropriate driver for the MicroLogix 1100 and 1400 controller is the "Allen-Bradley DF1 Master via PCCC/EIP" driver.
I just checked one of my Crimson programs, and I have the Network Protocol set to "Allen-Bradley DF1 Master via PCCC/EIP", and the PLC Device set to "ENI/Micrologix"
-Eric
He also has the G3 pointing to 192.9.200.52, and the G3's IP as 192.168.1.20... :unsure:
-Eric
Our colleague from Mexico's issue is simple: he needs to change to the "PCCC/EIP" version of the Ethernet driver for Allen-Bradley controllers.
But the issue touches on two anomalies in Crimson 3:
1. When you change the Driver, Crimson 3 changes the device IP address under that driver to 192.9.200.52.
That's a little weird. But it's easy to just go back and change it to what it was before.
2. When you change the Driver from DF1 Master to DF1 Master via PCCC/EIP, Crimson 3 may or may not completely thrash your tag database addressing.
What I mean by "may or may not" is that you can avoid this by performing a save-as-with-new-database-identifier before you change the driver. You can also export the tag database, change the driver, then re-import the tag database.
And what I mean by "completely thrash" is that I've had Crimson 3 change several tag addresses when I changed the driver. Some of them were simply offset by a few words, and some of them were changed to data tables that don't exist.
Even with its faults, I like Crimson 3 a lot. But the anomalies I have encountered (there have been others) make me very cautious when I use it.
Wow, I never realized that! Sure enough, when I reopened the original file, it was indeed set to 192.168.1.11. It got changed to 192.9.200.52 once I modified the driver.
Thanks for this info, Ken!... :site:
-Eric
Erick and Ken.
Thanks very much for your support.
I change the driver to Allen-Bradley DF1 Master via PCCC/EIP" and now is working the communication.
I enable the DHCP only to test and I forgot disable.
Again, thanks for your time.
Regards
hallo guy's, I have problem in comunication between PLC and SCADA. :shoot: I connected the plc with the scada and codesys due the keep server...
1,473
Hi everybody , I have to wonder if it is possible to exchange data and how. Someone knows where I can find material about? any help is...
1,738
well i have a issue in my job i need to comunicate one escanner dataman 8100 and one plc wago by codesys but i can't. i put the diferent protocols...
974
hi guys I just got a problem here, I set up the comunication between HMI and PLC, I could ping PLC from HMI, but they did not connect with each...
2,874
Hi guys I got a question about Barcode scanner and PLC: my SLC 5/04 will send some strings to a PC by using Channel 0, and a Barcode scanner also...
11,297