Hi Experts,
I've started a small hobby-project and for this I'm using a S5-115U. I'm using a programming software called PG-2000 (not a "real" Siemens product but it seems to work). I'm able to program the PLC without any problems, so far everything is fine.
Next step, I want to connect a few inputs to the PLC. I've a card with 32 * 24V inputs. I've connected 24 volts and the LEDS are reacting as expected. However, I imagine that I need to configure the hardware (what kind of cards that are connected to the rack). I can not find a setting for this in the software. Or do I need to program this?
All suggestions are very welcome!
Thanks!
//Supporter
S5-95U, S5-100U and S5-115U series didnt need much hardware setup. There was something in DB1, but most times you didnt need to modify it. From S5-135U and up you had to set dipswitches on the modules, but that is another story.
On S5-115U the addresses of the i/o is determined by the location in the rack. It is in the manual:
http://support.automation.siemens.com/WW/view/en/1085937
supporter said:
Hi Experts,
Thanks!
//Supporter
The S5-115 I/O was hard coded in the PLC memory.Each slot after the CPU has 32 bits of I/O which can be either Ins (I) or Outs (Q). If a 32 bit I/O is inserted all 32 bits available. If a 16 bit card is inserted only first 16 bits are available
first slot after CPU is addressed as:
I0 ( bits 0 - 7 ) or Q0
I1 ( bits 0 - 7 ) or Q1
I2 ( bits 0 - 7 ) or Q2
I3 ( bits 0 - 7 ) or Q3
next card :
I4 ( bits 0 - 7 ) or Q4
I5 ( bits 0 - 7 ) or Q5
I6 ( bits 0 - 7 ) or Q6
I7 ( bits 0 - 7 ) or Q7
next card :
I8 ( bits 0 - 7 ) or Q8
I9 ( bits 0 - 7 ) or Q9
I10( bits 0 - 7 ) or Q10
I11( bits 0 - 7 ) or Q11
hi all i am new here i have a mitsubishi smart touch hmi i.e ms-60t-pe but i cannot find a software to edit and download a program in it any help...
163
Hello, I am trying to connect a Stride Analog Output module to a 1769 CompactLogix via Ethernet. I added a new Generic Ethernet Module for the...
239
Dear all, I am beginer in ifix hmi programming. I have 2 ifix 6.0 pc with license FiX and client.. Can some one tell me how to configure sample...
150
Hi all, the machine I am programming the Rockwell PLC for has about 100 parameters that need to be adjusted for every customer. I would like to...
20
1,976
Within the last week or so, PME has crashed whenever I try to open a configure IO screen. I am running V8.0 Build 6215. Offline configuration of...
399