Control net issue
kratos1
May 2017
viet nam
25
Hi everyone. Please help me.
See attached picture is Rsnetwors for control net. Node 12 show: missing. I check cable connection is Ok. Control net Line A is green and in RSlogic5000 line A activated but network still fault with all devices in rack with node 12. In Rslinx also can’t find Node12.
Thanks for your support.
What kind of device is Node 12 ? How is its ControlNet node address configured ?
A solid green Channel A LED generally means that the device both is communicating on the network and has operating I/O connections. If there were no I/O connections active, the Channel A LED would be flashing green.
Is this an operating control system you are diagnosing, or is it a system you are starting up or modifying ?
Please post a general description of the system; screenshots only tell part of the story.
Please see attached file is rsnetwors upload and PLC configuration drawing.
This is an operating system. Before Control net line A is working, Line B not active because Line B from Coal bunker not connect. After We connect , Line B still not active and Red B flashing. We found 1 issue in Rslogic5000 config 1 rack with control net module is Node 15 but in fact that this is Node 13. I don't understand why we not have fault. After that I changed this config in Rslogic from Node 15 to Node 13 and download. This rack still work, Line B still not active but Node 12 fault.
We have solid green in A channel control net module and other IO green flash blinking.I can see in Rslogic5000 CN2R_N12.Channel_A_Active but not see this rack in Rslins.When I tried to Reschedule rsnetwors. I have warning Device in Rack 12 not respond..
Hi guys, I'm having an issue with a comms failure issue but I can't figure out the root cause. I've narrowed down the issue a good bit, and I'm...
19
12,249
Hey guys, I need an urgent help. I am setting up a control net network as per attached configuration. Can you please tell me how to configure...
2,805
So the customer purchased a Mitsubishi drive, in the same project for a different pump they got an ABB drive, was literally whatever they could...
71
Good day Forum Members I got a older Lincoln welder and hoping to make it work at our shop. Welder in question is the Lincoln Power Wave 455M...
235
An outside contracting firm designed a machine for our company. There are several devices connected through Ethernet/IP. This includes a Panel...
204
