Conversion
Lets simplify this, any time you have 2 values in a relationship it is called a "ratio'. In this case the ratio is 768 to 145, in other words 5.296 units per 1 unit i.e. at 3psi the plc would read 3*5.296 which would equal 15.88.
For any unit conversion on any PLC you can use four function math with the following, which
asumes integer math:
DataOffset = Data in input register at 4 mA (or zero analog signal of whatever range
- for example 0 VDC on a 0-10 VDC transmitter)
DataSPan = Data at 20 mA - Data @ 4 mA
FACTOR = arbitrary factor (multiple of 10) needed to get proper resolution and accuracy
EU = Engineering Units x FACTOR
EUOffset = Engineering Units @ 4 mA x FACTOR
EUSpan = (Engineering Units @ 20 mA - Engineering
Units @ 4 mA) x FACTOR
DATA = Actual data reading in input register
EU = ((EUSpan x (DATA - DataOffset))/DataSpan) + EUOffset
ProcessValue = EU / FACTOR
For Example, 0-60 psig from 4-20 mA with resolution of 0.1 psig:
FACTOR = 10
Data @ 4 mA = 6240
Data @ 20 mA = 31208
DataOffset = 6240
DataSpan = 31208 - 6240 = 24968
EUOffset = 0 x 10 = 0
EUSpan = (60 - 0) x 10 = 600
DATA = 18975
EU = ((600 x (18975 - 6240)) / 24968) + 0 = 306
Process Value = 306 / 10 = 30.6 psig
No answer, but a suggestion or two.
Cspatil,
Welcome to the Forum! I see that you already tried searching the archives for an answer, so at this point I would suggest you start a new thread with your question. Please also try to provide as much detail as you can. Such as what kind of PLC, what version of software, What exactly you are trying to multiply, ect..
One thing I would advise against is asking the same question repeatedly on different threads. It kinda clogs up the works. I'm sure if you start a new thread, and provide as much detail as you can, someone here will do their best to help you.
Will.
I have a machine which is undergoing upgradation. As part of the process two SEW drives are being replaced., existing Gen B with new Gen C. The...
230
Currently I’m using ESA model VT155W0000 HMI and it’s communicate with Fanuc PLC. Can any one suggest can I convert ESA model to EXOR HMI eSMART07M
117
hi... i have an issue in s7 300 plc, while we run the machine(in idle there is no fault) , plc cpu goes in SF mode, after restart the power cycle...
146
I have a Type C to RS485 adapter connect to my Siemens RWF55. I use modscan to scan it to get a value from the Siemens controller. In the...
119
Hi all, I'm in the process of upgrading a PanelView1200 HMI program to be developed in FactroyTalk View Studio. The filetype for PanelView 1200...
315