Conveyor speed
If you know the rpm of the drive wheel and the diameter of it you can calculate the speed. Maybe there are easier methods, but i never work with converyors.
Motor rpm. 1750
Drive pulley dia 4.5"
Driven pulley dia 22.5"
Gearbox ratio. 40:1
Drive sprocket. 15 teeth
Driven sprocket. 60 teeth
Head pulley dia. 30"
First thing is to figure out what the actual rpm of the drive wheel would be. Then the circumference because that will determine how much the belt will move in 1 turn (providing optimal transfer). and then calculate
Example, using metric here.
driving wheel, 10rpm
driving wheel circ, 0,5m
0,5*10=5m/min
5/60=0.08333m/s
[driven pulley dia] / [drive pulley dia]
Divide motor RPM by above result
Divide result by 40 (gearbox), save result
[driven sprocket teeth] / [drive sprocket teeth]
Divide saved result by sprocket result
This gives you the RPM of the head pulley
[head pulley dia] * pi (3.1415926) = travel per revolution (inches)
[travel per revolution (inches)] / 12 = feet travelled per revolution
RPM * feet travelled per revolution = feet per minute of belt driven by head pulley
If I'm interpreting correctly, you have a motor at 1750 RPM driving the input of the gearbox through a 4.5"/22.5" belt reduction.
The output shaft of the 40:1 gearbox drives the 30" diameter conveyor pulley through a 15/60 chain or timing belt reduction.
The input speed of the gearbox is 1750 * 4.5 / 22.5 or 350 RPM
The output speed of the gearbox is 8.75 RPM
The conveyor pulley speed is 8.75 * 20 / 60 or 2.91 RPM
The conveyor pulley is 30" (2.5 feet) in diameter and 2.5 * PI or 7.85 feet in circumference.
The surface speed of the conveyor pulley is 2.91 (Revolutions per minute) times 7.85 (feet per revolution) or 22.9 feet per minute.
I'm coming up with a different result than guy below you aabeck
Nevermind I'm an idiot. Thanks guys I appreciate everything!!
Hello everyone. I have a feedback from encoder to measure the speed of conveyor, if in need to control the speed of the conveyor to a preset...
1,902
I need help on develping PLC logic to use a PE(photoeye) to detect and calculate the lenght of parts and gap between parts on a conveyor. Conveyor...
5,327
I am designing a concrete mixing plant and require about 6 different speed pulses to determine speed of the 6 conveyors. The maximum speed is 3...
1,321
Hi,all: we have over head chain conveyor drove by PF525,the total conveyor length is about 1350 foot, its speed jumping too much (not stable)...
30
6,314
I have a conveyor whose speed varies between 20 and 50Hz through a PLC (HMI). I need to program a code with a timer whose value will vary between...
26
4,454