Jeff
IF my installation I would size CTs for the main breaker ie 700 amp.
Generally the secondary current is 5 amp at full load ie 700, therefore you have a 700:5 CT.
To make the math a little easier assume 750:5 CT -- at 150 amp it would "deliver" 1 amp.
Resolution is a little hard to understand and commonly confused with accuracy. Compare to a target ie bullseye. Resolution means you hit the same spot every time EVEN if it is the wrong spot. Accuracy means you hit the bullseye - when you aim for it of course. So with good accuracy and good resolution in theory (disregard wind and barrell heating etc etc) all bullets will go thru the same hole in the target.
SO with good resolution and rated at say 1% the 750:5 at 750 amp
output is +/- 0.01 amp.
With good accuracy then output is 1.00 +/- 0.01 amp.
If accuracy is off by 10% high output is 1.1 +/- 0.01 amp.
I think I have it right -- anyone care to correct me if wrong?
Dan Bentler