Hello,

I have a device with 68 words input.

But one block on the Devicenet Scanner is only 61 words.

I am trying to map this device to 2 different block, block 62 and block 61

61 words in the first block and the remaining word in the second block.


I can't seem to find a way to do this, I can map starting from byte 121 to the beginning of block 61, but then when I try to map the remaining bytes, the system shows that it is already mapped.


Any idea? Or I just have to double up on my device node.

Dn_screen.png
 
For those of you unfamiliar with the PLC-5 DeviceNet scanner, it had a much bigger memory than most modules. The way that you could distinguish chunks of that memory in the program is by the size of the Block Transfer instruction used to transfer it to and from the PLC-5.

The most important cheat sheets are on Pages 19 and 21 of the User Manual. It's hard to do tables here on PLCTalk so I'll summarize that the status data and mapped field device Input data are accessible via block transfers:

BT 62 holds the Module Status Register in Word 0
BT 62 also holds Words 1-61 of mapped input data
BT 61 holds Words 62-122
BT 60 holds Words 123–182
BT 59 holds Words 183–241
BT 58 holds Words 242–299
BT 57 holds Words 300–356

There are no BT's 56,55,54,53

BT 52 holds the Device Failure Table
BT 51 holds the Device Active Table

If you want less data, a BT sized 1-50 will return the first 1-50 words that otherwise would have been in BT 62.

--------------------------------------------------------------

Now, back to the application and how RSNetworx gets tricky with units and offsets.

You should be able to map 61 x 2 = 122 bytes of field device input data into Block Transfer 62. Remember that the first word of BT62 is reserved (styled "Read Only" in the PLC-side address display) for the sixteen-bit Module Status Word.

So that's the first map segment in the Advanced Mapping window: the polled data starting at Byte 0, going into the available input data section of BT62 starting at Byte 0. The Length in bits is 122 x 8 = 976 bits.

I don't like that it says the target is "Byte 0 Bit 0" of BT62, because the first word is actually reserved and addressed to N9:0 over on the left, but that's how it works. The first word of data from the NT100 will go into N9:1.

Then you should be able to map the next 7 words of data (you have a total of 68 words = 136 bytes = 1088 bits) into the first 7 words of BT61.

So the second map segment should start at Byte 122 of the Polled input data, and be mapped to Byte 0 of BT 61, length 7x2x8 = 112 bits.

It's late and I don't have scratch paper or an illustration tool, but that makes sense to me.
 
For those of you unfamiliar with the PLC-5 DeviceNet scanner, it had a much bigger memory than most modules. The way that you could distinguish chunks of that memory in the program is by the size of the Block Transfer instruction used to transfer it to and from the PLC-5.

The most important cheat sheets are on Pages 19 and 21 of the User Manual. It's hard to do tables here on PLCTalk so I'll summarize that the status data and mapped field device Input data are accessible via block transfers:

BT 62 holds the Module Status Register in Word 0
BT 62 also holds Words 1-61 of mapped input data
BT 61 holds Words 62-122
BT 60 holds Words 123–182
BT 59 holds Words 183–241
BT 58 holds Words 242–299
BT 57 holds Words 300–356

There are no BT's 56,55,54,53

BT 52 holds the Device Failure Table
BT 51 holds the Device Active Table

If you want less data, a BT sized 1-50 will return the first 1-50 words that otherwise would have been in BT 62.

--------------------------------------------------------------

Now, back to the application and how RSNetworx gets tricky with units and offsets.

You should be able to map 61 x 2 = 122 bytes of field device input data into Block Transfer 62. Remember that the first word of BT62 is reserved (styled "Read Only" in the PLC-side address display) for the sixteen-bit Module Status Word.

So that's the first map segment in the Advanced Mapping window: the polled data starting at Byte 0, going into the available input data section of BT62 starting at Byte 0. The Length in bits is 122 x 8 = 976 bits.

I don't like that it says the target is "Byte 0 Bit 0" of BT62, because the first word is actually reserved and addressed to N9:0 over on the left, but that's how it works. The first word of data from the NT100 will go into N9:1.

Then you should be able to map the next 7 words of data (you have a total of 68 words = 136 bytes = 1088 bits) into the first 7 words of BT61.

So the second map segment should start at Byte 122 of the Polled input data, and be mapped to Byte 0 of BT 61, length 7x2x8 = 112 bits.

It's late and I don't have scratch paper or an illustration tool, but that makes sense to me.

That was it!, I missed the field where I have to specify the bit length to go along with the starting word location.

Thank you Ken!
 
You have to be a little impressed with a software tool that manages to combine 16-bit, 8-bit, and 1-bit fields in a single window.

Between the complexities of RSNetworx and the Hilscher tool, you should spend some time making maps and comments about what data goes where and how, so that future programmers can make sense of it.

Glad you got it working !
 

Similar Topics

Customer has a circa 2004 SLC-500 PLC. Fieldbus is a 1747-SDN DeviceNet scanner. Customer has SLC-500 file (.rss) with no comments. Has no *.dnt...
Replies
7
Views
562
Hello, I am setting up for practice and I am having trouble seeing the 1771 Scanner in RsLinx as well as Rsnetworx My setup: slot 0 : PLC-5/40E...
Replies
3
Views
978
Does anyone know the part number for that plug that plugs into the 1771 devicenet scanner? The manual just says it is a linear plug, its 5 pins.
Replies
3
Views
1,054
Hello, I'm trying to replace a 1769-SDN devicenet scanner on a compactlogix system. The issue i'm having is when i replace the scanner and...
Replies
1
Views
1,885
Hi all, Our cell was running ok then our scanner dropped out with error 80 idle mode. We got it running again but not sure what is causing it to...
Replies
4
Views
3,537
Back
Top Bottom