Good Morning,
I got an IMO HD2 inverter with 2 slots and on the first slot I put the ethernet module (HD2-E-ENET) and the second one is free.
LED indicators on the module:
LED 1: Green Blinking 1 Hz
LED 2: Green
LED 3: Red Blinking 4 Hz
LED 4: Green
I’m following the hd2ethernet manual (hd2enetmanual.pdf (imopc.com)) from page 31 regarding Ethernet IP communication card to configure it and configure the PLC studio 5000 settings.
On the inverter I have as suggested by the manual on page 34:
"If you want to control the VFD with the communication card, set the control mode to
EtherNet/IP communication control. To be specific, set P00.01=2 (communication as the
running command channel) and set P00.02=3 (EtherNet/IP communication channel) to control
VFD start and stop"
I’m trying to connect this module to the Allen-Bradley plc (1769-L16ER-BB1B), but it is resulting in fault status.
I have made sure that the ip address are correct (plc ip address 192.168.1.210, inverter ip address from P16.02-P16.05: 192.168.1.222)
I can ping the inverter from the pc.
I tried both ways, connecting the inverter directly to the plc and with an ethernet switch, in both ways pc can ping it but plc seems not to see it.
Please see the attach picture to see my plc configurations.
Can you please tell me what the problem could be?
Thank you.
I got an IMO HD2 inverter with 2 slots and on the first slot I put the ethernet module (HD2-E-ENET) and the second one is free.
LED indicators on the module:
LED 1: Green Blinking 1 Hz
LED 2: Green
LED 3: Red Blinking 4 Hz
LED 4: Green
I’m following the hd2ethernet manual (hd2enetmanual.pdf (imopc.com)) from page 31 regarding Ethernet IP communication card to configure it and configure the PLC studio 5000 settings.
On the inverter I have as suggested by the manual on page 34:
"If you want to control the VFD with the communication card, set the control mode to
EtherNet/IP communication control. To be specific, set P00.01=2 (communication as the
running command channel) and set P00.02=3 (EtherNet/IP communication channel) to control
VFD start and stop"
I’m trying to connect this module to the Allen-Bradley plc (1769-L16ER-BB1B), but it is resulting in fault status.
I have made sure that the ip address are correct (plc ip address 192.168.1.210, inverter ip address from P16.02-P16.05: 192.168.1.222)
I can ping the inverter from the pc.
I tried both ways, connecting the inverter directly to the plc and with an ethernet switch, in both ways pc can ping it but plc seems not to see it.
Please see the attach picture to see my plc configurations.
Can you please tell me what the problem could be?
Thank you.