This subroutine L0.0 when set?
(A9K5}XJI_4N`T2}Y`EA@ON.jpg


L00.jpg
 
L0.0 will be true when the rack fault occurs. OB86 will also get called when the rack fault clears but this time L0.0 will be false.
 
}@_UD1G{NQWS2R9EN3P@{2D.jpg

How to determine is the L0.0 do? thanks
I just started learning S7-300,My project S7-300 DP PROFIBUS 6se71.
 
That is just the S7-300 rack, not the inverter the 6SE71 of PROFIBUS failure? This fault me how to troubleshoot it?
 
OB86_EV_CLASS OB86_FLT_ID Meaning
B#16#39 B#16#C1 Expansion rack failure?OB86_MDL_ADDR: Logical base address of the IM?OB86_Z23: Contains one bit for each possible expansion rack: Each expansion rack that caused a call of OB86 is reported as having failed (the respective bits are set). Expansion racks that previously failed are no longer shown.- Bit 0: always 0- Bit 1: 1st expansion rack- :- Bit 21: 21st expansion rack- Bit 22 to 29: always 0- Bit 30: Failure of at least one expansion rack in the
SIMATIC S5 area- Bit 31: always 0
For example, this type do you mean?
 
L0.0 TRUE means that either a remote Station has been disabled using SFC 12 - OB86_EV_CLASS = 16#33 - or that a rack fault has occurred - OB86_EV_CLASS = 16#39 - and the error type and rack number are held in OB86_FLT_ID.
 

Similar Topics

We had a site where a rat gnawed through some fiber optic cables which (obviously) prevented communication to a remote rack entirely. We, and the...
Replies
3
Views
95
Good morning everyone I’m currently working on a omron device net and have a nord drive that fell off the network. I have limit knowledge in...
Replies
2
Views
90
Hi. We've been asked to do an upgrade on plant, consisting on a PLC upgrade. This involves replacing a 1747-SDN module to a 1769-SDN, in a network...
Replies
0
Views
69
in allen bradley kinetix 300 drive first E31 error shows after resting drive E11 error occurs need solution to reset E11 fault code
Replies
4
Views
160
All, I have a PowerFlex 525 driving an agitator motor. The goal is to have the agitator start automatically after a power loss or a comm loss. I...
Replies
2
Views
107
Back
Top Bottom