Hi guys, long time... :)
I've been recently tasked to get some new mag flowmeters working in our Paint Mix room, and we ran into problems because the new paint that we are using has nearly zero conductivity. Oops...
So, now I'm trying to come up with something different. My ChemE buddy suggests going ghetto and rolling our own orfice plate flowmeters. Based on the info below, what size orfice would you suggest?
And the math formula for calculating the flow would really be nice as well. :)
BTW, the piping is 1", flow is between 10 - 25 GPM, and pressure is usually around 150 PSI. But all we really care about is flow.
As for accuracy, it's not that important. Even 25% off isn't any big deal.
I've included the paint specs (sorry about the excel spreadsheet, trying to post it within the message didn't work out so well).
If you need any other info, just let me know.
Thanks in advance,
John
Orifice sensing is differential pressure technology.
The impulse lines from the flange unions to the dp meter are dead headed, no flow through them. Is there the possibility of the paint aging or curing and blocking the impulse line?
Will you have to clean the impulse tubes/pipes between batches to keep any residue from mixing?
Dp's work great on media like steam, water, heating oil, gases, that doesn't clog or need cleaning. Does paint qualify?
Is the CPS column the viscosity values?
#2 is clearly different than the others.
Without a sizing program it's difficult to say how far off you're going to be for any different product from the design conditions.
By the time you buy a dp meter, orifice flange union, & an orifice plate, you aren't that far off from the cost of a thermal flow meter which is tube with a couple small protrusions in it, not that different than a magmeter.
Or even a paddle wheel meter (note the fairly significant pressure drop)
http://www.koboldusa.com/flow/us_df-k.htm
Here is a range of liquid flow switchs I have used that may suit you, one has a basic analog output, as well as a switch operation.
Its effeectively 2 thermistors as a differtial temperature sensor, one is in touch with the stainless steel tip, whilst the other is near, but is insulated from the tip, so the greater the flow the greater the temperature difference.
http://www.ifm-electronic.co.uk/ifmuk/web/pselect2!2_30_10_30.html
John
I ask mostly out of curiosity.
Other than confirming the pump is pumping what are you going to use this data for? A tolerance of 25% does not seem to justify the time trouble or cost.
Dan Bentler
If all you need is flow then a low cost mecchanical meter with a pulse output will probably be fine but a higher spec instrument could open up all sorts of possibilities for improved control. A good coriolis meter could give you pressure, temperature and viscosity readings as well as flow so the extra expense might be worth considering.
Andybr
I think of paint as high solids and potentially plugging orifice or any similar differential pressure type meter. How about ultrasonic? There are strap on ones available so you may not need to penetrate the pipe.
Ultrasonics are pretty expensive. As long as the line is never open to the air I would go with a turbine meter and pickup arrangement or a thermal flow meter as already suggested. A coriolis is the cadillac solution but its also one of the most expensive.
I think orifice and dp will have clogging problems with paint pigment build-up so I wouldnt go that route, or any route involving small holes and differential pressure impulse lines.
Simple and cheap there is always a rotameter with an external sensor arrangement. Theyre nort particularly accurate but they are cheap!
Last and by no means least theres always a PD meter. They seem able to cope with pretty much anything you throw at them and theyre pretty cheap and super accurate.
Not generally, no. But the meter is directly ahead of the filter anyways.
We don't do "batches", each color has its own tank to pull from (the color change is done in the robots). So it shouldn't be a problem.
Pretty much, but our low flow rate and our high viscosity seems to be a problem (to the meter salesmen at least).
Yes.
It's a Fisher #2 cup measurement. It's a cup with a hole in the bottom that restricts the paint as it drains out. The value is the number of seconds that it takes for the cup to empty.
It's going to be trial and error, especially if we make our own. But we do have the textbooks here that have the formulas...
I just got off of the phone with a thermal flowmeter apps guy. They don't have a solution for anything other than gas. I've got a call in to a different company, and I should hear from them tomorrow.
That's what our competitor up the road uses. :)
Thanks for the help, I'm hoping that the thermal flowmeter works for us.
OkiePC said:
We use a turbine type flowmeter from Great Plains Industries that is very reliable and accurate, and extremely simple.
Our application is water, but their website claims a wide variety of fluid applications.
I gave them a call, but it's after hours. I'll try again tomorrow.
http://www.c-a-m.com/content/vm/flo/index.cfm
MEASUREMENT SYSTEMS
REGIONAL SALES OFFICE
302 TOLEDO DRIVE
LAFAYETTE, LA 70506
UNITED STATES
Contact: DANNY MCFARLAND
Phone-1: 337-234-1824
Fax: 337-232-1580
I dont think they service your area but this guy can probably help you see if they have something that will work in your application.
Which one was the thermal flowmeter? I found the mag meter.
The vibration meter for the motor looks interesting (different app obviously).
Thanks!
leitmotif said:
John
Dan Bentler
That's the $64K question. Do we really need this info, or is it a leftover from the way that we used to do business? I haven't got an answer to that one as of yet.
As for 25%, that's more of a reality-based threshold than anything else. I'm willing to let the accuracy suffer for something that will work for us.
Good question though, now if my bosses would just come up with an answer for it... :)
Andybr
I had the MicroMotion (coriolis) guy down here today. It would be perfect, but at a cost of $7500 each (ouch).
Thanks. :)
I was told that the ultrasonic requires a goop not unlike what the doctor uses for an ultrasound.
Since it's a clean-room environment, that's a non-starter for use (if we located it outside of the Paint Mix room then that would be another story).
Thanks. :)
Is it good idea to use ultrasonic clamp type of flowmeter for water dosing? I already using the flowmeter pulse output by setting to 10L per...
1,300
E+H Promag P500 5069 Compact Logix implicit Ethernet IP using endress device description 30ish flowmeters, every time I download, some (but not...
1,277
Having an issue with network timing out when trying to use CIP generic on a Micrologix 1100 B. I’m trying to read flow and totalizer information...
19
5,100
Hi All, E+H Promag W 500, 5W5B1H (Ethernet I/P implicit messaging 500ms) AB 5069-L330ER v33.01* I have a customer requirement where I need to...
1,419
Hi everyone, I have been looking for a while a flowmeter for soybean oil. I have already tried wheel type and gear type with not good results...
1,028