FT View SE 13 Alarm and event log database error

vaibaras

Supporting Member
Join Date
May 2014
Location
Kaunas
Posts
4
Hello,

we have two PC with the FT SE local application and the same project. The one PC is wrong about alarm and event log.

When I open the alarm log page it doesn't show nothing only: "Lost connection to alarm and event log Alarms"
In another PC the same project working properly.
SQL database is ok, all settings is Ok.


FT diagnostics viewer shows: some errors, see attachment.
What is problem?

IMG_7253.jpg
 
The last log in your image is the clue. You have connectivity issues between the non working PC and the PC retaining the database.
 
thanks for answer. I have checked all settings, compared with another PC, but always get message Lost connection to alarm and event log. Maybe you have some ideas?
 

Similar Topics

Hi folks. I have a system that I'm working on that needs 2 alarms banners with different event subscription: - One banner for a specific area...
Replies
0
Views
44
This may be something obvious that I could learn if I sat down to understand the topic in detail with tutorials and manuals. But sometimes it's...
Replies
0
Views
137
I have a issue with my alarm summary/banner where it losses connection to the Alarm Server. It's kind of weird because when I click on the server...
Replies
2
Views
1,369
Hi, I am having some issues with FactoryTalk View SE (Local) Alarm and Event server. In my "active" alarm windows all alarms is shown correctly...
Replies
0
Views
978
Hi all, I have a network distributed FTView SE system, which has three clients, showing alarms for three different sections of plant. I have...
Replies
3
Views
4,477
Back
Top Bottom