Hello All,
I have an 1756-L72 ControlLogix Processor (V20) with an 1756-EN2T Ethernet card. I have added a Generic Ethernet Module to talk to a device over EtherNet/IP. I am communicating with it fine. I need to detect if the I/O connection is healthy. If the unit looses power, I see the yellow triangle with exclamation mark on the Generic Ethernet Module I added in the I/O Configuration tree in the controller organizer. I also see the status of the module go from running to communication timeout. The message of which I/O is missing also scrolls across the message display on the processor. All these things are great but I need a bit i can monitor that I can use to set an alarm to the operator. Is there a way to get the connection faulted status of a Generic Ethernet Module into the PLC register?
Thanks,
Lovell
Use a GSV instruction to query the module itself within your project:
GSV Module "ModuleName" EntryStatus "Some_INT_Tag"
If the resulting code is anything other than 0x4000, you'll need to consider action. Check the Logix Designer help.
Trying this now:
That logic can be simplified by eliminating the BTD instruction and changing the NEQ and EQU instructions' A operand to 'Module_Status' itself and the B operand to 16#4000, but the result is largely the same.
You're welcome. :)
Hello, We are having trouble setting up a generic ethernet module for a Yaskawa GA80U4168 drive in RSLogix 5000 Version 20.01. All of the...
612
Hello all, I need to add a module in logix for an SMC pneumatic valve manifold specifically EX600-SEN3/4. The eds files I add crash the program...
679
So Rockwell PLCs have some generic ethernet module options available in the IO tree configuration. With the standard generic ethernet module, you...
733
​Hello everyone, I triyng to link a Power Module eMB-60R from Robot Adept Viper s650 to CompactLogix, version 19.11 I followed exactly the...
2,655
Hello: I have not been able to get RSLogix 5000 to display expected configuration screen for 1732E configurable armour blocks. Waiting for RA...
39
12,423