Good day,
I know my question is a basic when using a PLC.
Can someone please tell me how do i select the right power supply for my PLC
how do i know if i will use, for example, 1769-PA2 or 1769-PA4. I am using a 1769-L35CR power supply with 1 1769-OB32 and 2 1769-IQ32 and 1 1769-IF10 thanks for your help in advance. :sick:
There are rules for Compact Logic power supplies. (Read the manual).
The one rule people forget is the 50/50 rule. A 1769-PA2 supplies 2.0 amps, but only 1.0 amp to the LEFT, and 1.0 amp to the RIGHT; a 50/50 split.
So, you might have to move your modules around, to match the load to the power supply.
Again, the manual shows all the detail on how to do this.
Please explain this statement, cause I don't see the reason, specially for small power supplies. Power supplies we are talking about are voltage generators, so there is constant voltage, not constant current. Components inside unit should be far from one amp if producer is serious one. If it is stated 2.0A but with 50/50 split, it should be written.
I don't say that your are not wright, but that I don't see the reason.
Also to say, that it is very good practice to leave at least 20% reserve.
Goghie,
The 1769 power supply literature does a good job explaining the power supply limits, and the 1769 selection guide includes the current draw and distance rating of the IO modules and Processor. You can find these manuals at www.ab.com/literature.
However, it's often the case the folks will just buy the larger supply versus running the calculations.
The way I size 1769 power supplies is using the free IAB tool from AB.com. It's a big download but I use this software almost every day to build PLC boms.
Hope this helps,
Shawn
I am facing a very strange issue with the AB hardware, specifically with power supplies. The problem started when a power supply in a 4 slot...
4,141
Dear sir. We are in the engineering stage of our project..I want to submit material submital to client.. In that complaince statement as per...
3,700
Hello, Sorry this is a little off topic, but here is my problem. I am using a Direct Logic DL06 plc and a Rhino PSM12-078S (12V 72W 6A) power...
4,694
U
hi, can any one tell me if the Sitop power supply by siemens model 6EP1336-2BA00.rated 120/240VAC, 8.0/3.3A on the input and 20A, 22.8VDC-26.4VDC...
1,437
Unregistered
U
hi who can find for me INDRAMAT TVD 1.2-08-03 AC SERVO POWER SUPPLY Tnx a lot Karen.h
7,126