Help with S5 output card
bitmonkey
Oct 2015
Ohio
94
Hello,
I have tried searching the web and have so far been unsuccessful finding any documentation on this particular output card. Specifically what I'm looking for is information about the red light at the top of the card. It appears to be a Fault light indicating that 24vdc is not available to the card? Just my guess, but the light goes on and off when the machine is running as if it's being controlled by the plc???
Thanks guys!
Any chance you can type in the part number on the card?
Manufacturer?
(I can't read the numbers on the front of the card.)
Also, did you try metering the 24 V supply while the machine is running?
(I had a machine once, the 24 Vdc would drop out while the machine was running,
then come back on again . . . New supply fixed it.)
Poet.
Also yes I did meter the 24v and it was low, around 19-20 v. I adjusted it up to around 21-22 volts, which did seem to improve overall reliability, but the light still goes on and off while running. When the light is on, the machine won't run.
So I finally got to the bottom of this issue. It turns out that one of my outputs was being intermittently backfed 24vdc from a bad switch that was paralleled with the output, causing all kinds of problems. There was nothing wrong with the output card.
I have a Mitsubishi FX2N-64MR-UA1 processor. The 1st analog output card is an FX2N-4DA. It requires 24VDC power. That card is obsolete. The card...
1,589
ok i have already my project in RS View Studio ME, the problem is that I have to connect an analog output card to send a measurement of pressure...
5,558
Hi, I work in a brewery in North Carolina and I need some help finding the output current for a VFD in the PLC. First off I am new to working with...
1,337
Hi all! I have one question, it might be simple for one of you but I spent hours searching and reading through different platform until I found...
1,645
Hey guys, I'm a novice programmer and looking to learn how to create logic for an analog output to control a VFD. I've taking the Logix Designer...
2,095