Help with wiring ML-1000 L32BWA
spyder905
May 2006
Toronto
Hey guys,
I am fairly new to plcs but am putting the hours in to remedy that.
Anyways, I recently got my hands on a Micrologix 1000 L32BWA.
I am unsure of how to wire up my outputs so thought I'd see if I could get any help here.
I need to use 24VDC outputs so how do I wire that into the controller? I thought the BWA model uses AC relay outputs but I see VAC/VDC labels over the outputs so I now I am not sure.
So my question is, can i wire my ouputs using VDC or am I out of luck and would need to get a L32BWB????
Hello,
They are relay outputs, therefore will switch whatever voltage type you connect to the common. You are ok to use AC or DC (y)
Hope this helps....
Ok thanks a lot guys.
I read through the manual but wasnt 100% sure. I really, really dont want to fry anything.
Sorry, but there are just a few more things I want to clarify before I connect everything and run my program.
1) As on pg 45 of manual, I connected my dc source to the commons of all the outputs. I have left L1 and L2/N empty as Im not using AC. Is this correct??
2) Im using a 24V power supply for my outputs. If I needed 5V outputs could I use a 5V power supply or must be 24V??
Thanks again, stupid questions I know, but just trying to cover any of my doubts so nothing goes wrong
1. Very few questions are stupid. But you said "I have left L1 and L2/N empty as Im not using AC." Since this PLC RUNS on AC power (85-264 VAC as the label shows) exactly what do you expect it to do without power?
2. This is a RELAY output PLC. That means it will attempt to switch any voltage you apply. Virtually all AC or DC references to a relay I have seen are to the coil of the relay. You aren't attaching to the coil, only to the contacts. The output range for the contacts on the BWA shows 0-264 VAC (with 0-5 VAS not recommended) and 0-125VDC (again with 0-5VDC not recommended).
3. Whatever voltage you apply to the commons (labled VAC/VDC) is the voltage which will be switched to the contact(s) to the right up to the next "VAC/VDC". This is an output group. You can use AC on one group and DC on another group (as the diagram shows).
Hi guys, We've got a small project of converting an SLC 150 (1745-LP153) into MLX 1000 (1761-L32BWA). Appreciate it if you guys can help me on...
7,360
Im a mechatronics instructor at a local community college. I have a couple of motor control questions and would definitely appreciate any help...
1,797
https://imgur.com/a/kKPtzyP We are making improvements to these motor controls by replacing these old resistor banks and DC generator with DC...
1,789
I intend to use a clickPLC to turn a motor on and off for predetermined times. I am still very new to this and not sure exactly how I wire...
1,536
Good morning folks, I need your help and I am a beginner on PLC and I have been given an assignment on wiring a flowmeter to plc and create a...
2,222