My wild guess is that there's another object on the screen (it would take just one) that addresses a non-existent data table file. When the PV+ changes to that screen, it tried to start polling that address and gets an error, but because it's a serial connection there's not enough "bandwidth" to accommodate the attempts, errors, retries, AND the normal connectivity. The whole optimized block comms falls apart.
Maybe when the co-worker re-addressed all of those objects they remedied a typo, maybe working too fast to realize it.
This kind of error *should* show up in the FactoryTalk Diagnostics display object, and/or in the FT diagnostics display window of FTView Studio if you test the runtime on your development PC.
Or, sunspots.
Maybe when the co-worker re-addressed all of those objects they remedied a typo, maybe working too fast to realize it.
This kind of error *should* show up in the FactoryTalk Diagnostics display object, and/or in the FT diagnostics display window of FTView Studio if you test the runtime on your development PC.
Or, sunspots.