Good morning, this is my first posting on this site.

I am trying to configure alarm and event messages without Pdiag on an OP37 with simatic S7

My plan was to load a value into a word in the PLC when A certain state is active in the program.

Does anyone know how to configure a screen or message area to display a certain message depending on a word value.?

Is there another way of configuring alarms/events and text without using Pdiag.??

appreiate anyones help

kind regards Neil Stokes
 
Hi,

In your Protool project:

Area Pointers > double click that > in pop up box select Alarm Messages > Hit OK > Next screen select the connection and where the alarms are located. ie M for Flags, DB if you use a DB. Select which DB if using DB. Select offset ie DB1 then 100 is DB1.DBW00 starting point. Then select how many words you want. And the Acquisition cycle.

Once this is done, go to Messages > Double click on Alarm Messages. Now you can enter your alarms. Do note on the bottom right, on the status bar, you will find a small window which shows the memory location in the S7-PLC of the currently selected alarm.

After all the alarms have been created, now you need to create a button or other event to summon the alarm window.

And thats basically it.....

Oh wait. Just re-read the post. Isn't going to work with values. Well not directly. Alarms are bit triggered. Multiple alarms can be triggered simultaniously though.
 
Neil stokes said:
Good morning, this is my first posting on this site.

I am trying to configure alarm and event messages without Pdiag on an OP37 with simatic S7

My plan was to load a value into a word in the PLC when A certain state is active in the program.

Does anyone know how to configure a screen or message area to display a certain message depending on a word value.?

Is there another way of configuring alarms/events and text without using Pdiag.??

appreiate anyones help

kind regards Neil Stokes
Use the top of your screen.
Add a message display and display text according to a value of a word in the PLC. The display should be setup as a multistate indicator actually. A decimal value will trigger a different message.
The top of your screen contains an active-x window I think, which means, once you set it up it will be displayed on every screen the operator is on.
As far as alarms, do as Jeebs suggested.
 

Similar Topics

Is there are standard for what an alarm or fault message must say? More specifically, what details must be supplied in a fault message? For...
Replies
32
Views
6,958
Hi I'm trying to make messages cycle on a display. My marker double word holding the messages is MD100. If I have more than one bit of MD100...
Replies
4
Views
1,845
hi there, I'm a beginner pls help when transferring pc to hmi there's an error message on shihlin hmi written com1 station 1: communication...
Replies
1
Views
72
Hello, I have a Mitsubishi FX3G 14M PLC and a E615 HMI from Mitsubishi/Beijer. I'm using GXWorks 2 to do the programming and I have no problem...
Replies
4
Views
149
Good people of PLCs.net, I am currently working with an HMI that is advantech 1250H, that communicates with a 1769 Compact logix and Currently...
Replies
2
Views
79
Back
Top Bottom