How to find out max Frequency for an input?
skyfox
Nov 2006
CA
279
PLC is a L24ERQB1B. Embedded inputs are not high speed. RPI for these inputs are currently set to 20 milliseconds and program scan time is > 1.5ms and <2ms. If I drop the RPI to 1.5 milliseconds for the inputs ensuring each scan sees a fresh update from the input card, how do I go about figuring out what the maximum number of pulses that one of these inputs can detect reliably in a given second?
According to theory from Nyquist, you need to sample the signal at least double the frequency of the highest signal frequency in the sample. Your data only updates every 20 milliseconds, or 50 hz. The fastest signal is half that, or 25 per second.
Thanks proof,
Appreciate your help. Does that mean I Can reliably sample 250Hz pulse rate if I set the RPI from 2ms to 2ms which would give me 500Hz? What determines the RPI limitations on a given module. i.e. How can I find out the fastest RPI I can use for a module in a given system.
Thanks proof,
Don't you loose half again if your scan time is up to 2ms and RPI is also 2ms? Nyquist again. Down to 125Hz
Dirt,
Since RPI and scan times are independent of each other, shouldn't I be able to get a fresh update from the input each SCAN (at 2ms) and therefore be able to scan a 250hz input? Or am I missing something here?
Hi All, Got called into a fiberglass factory yesterday, had to go back today. Yep,I itch! They have a Versamax IC200UDD164 operating a stepper...
2,052
hi. i have a problem. im using omron cx-programmer..how to write the program to find maximum and minimum value in ladder diagram using the...
3,267
Hi , Where i can find Mitsubishi PLC Card end of line & replacement model details. i am looking for Q02CPU replacement model. Please advice. thanks
126
I have tested every screen and no single screen individually has this fault pop up, but when I compile and send to the PanelView it comes up. If I...
180
Hi, One of my customers has an old fabric tensile testing machine. The IC # AD7501KN of its controller has malfunctioned. This IC is related to...
84