Humidity transmitter wiring help
MGuenette
Jan 2007
Montreal
134
I want to connect a RH transmitter on a 1746-NI8 card on my SLC500.
I'm just a little bit confused about the wiring
Here's what I have :
If I understand I need to connect :
  • +24VDC on the power connecter on the RH transmitter (coming from 24VDC pôwer supply for exemple)
  • Wire from OUT on the RH transmitter to the Input+ on my 1746-NI8 card
  • -24VDC to the INPUT- connecter on my 1746-NI8
  • Make sure that my input is in 4-20mA mode. (DONE)
I think that part is clrear, but is the 1746-NI8 card will support 24 VDC??? I connect the RH transmitter like that, I will have 24 VDC on the OUT connecter on the transmitter and then connected on the SLC card.
Martin.
yeah you have it, that will work. i am not sure about your question regarding the support of 24v DC? this type of card can handle that voltage level.
cheers
myles
Sounds like your humidity transmitter sends a signal only when its in range if it was sending analog data on the output the range would not be 24 vdc standard ranges include 4-20 ma 0 to 10 volts -5 to +5
(-20 to +20 -10 vdc to +10 vDC) these are the ranges on the 1746 NI4 card
acceptable ranges are usually written on the card I don't have an NI8 version of card to check that but I don't beleieve I've ever come across a 24 vDC analog range
Thank you very much for your quik response!
Really appreciated. I will connect my sensor today
Thanks again
Have a nice day
Martin.
I'm very new to the plc game. My newest experiement is to wire up the Omega hx93 humidity and temperature transmitter to my slc 5/03 processor 7...
3,871
I am looking for temperature/humidity sensor recommendations. Would like the sensor to display temp and humidity. Need to connect to a Contrologix...
262
We've had a number of design discussions and done some extensive testing on enclosure heating/cooling solutions for various panel builds...
708
For you instrument people. I'm using a PLC, VFD, and HMI for climate monitoring and control. Automation direct has combo Humidity and Temp sensor...
2,042
Does anyone know of a sensor/transmitter that is able measure humidity/dewpoint/water concentration in a stream of 1200F air?
3,442