Hardware: 5069-L320ERMS2
Software: Logix Designer 35.11 / Ignition 8.1
Issue: When attempting to write to the tag "HMI_DRV200_DynamicTrim" in ignitition, the tag write returns "GOOD" but the value does not change. If i disconnect the OUT of the following AOI from the tag, the value will change when writing from ignition. To my confusion, disabling the routine (not calling it with JSR), will not allow the value to update via ignition. I assume i need to go about this differently and that there is no actual software issue, but I'm not sure exactly why the value does not change when writing.
*EDIT* I've found that i can't ever change the value of the tag in Logix Designer itself unless i disconnect this tag from the AOI's OUT
Software: Logix Designer 35.11 / Ignition 8.1
Issue: When attempting to write to the tag "HMI_DRV200_DynamicTrim" in ignitition, the tag write returns "GOOD" but the value does not change. If i disconnect the OUT of the following AOI from the tag, the value will change when writing from ignition. To my confusion, disabling the routine (not calling it with JSR), will not allow the value to update via ignition. I assume i need to go about this differently and that there is no actual software issue, but I'm not sure exactly why the value does not change when writing.
*EDIT* I've found that i can't ever change the value of the tag in Logix Designer itself unless i disconnect this tag from the AOI's OUT